I have a current project that is an assisted living (I-1), Type VA,1 story, fully sprinkled NFPA 13 (dry system), 13,665 sf, built in 1999. Its a typical H-design assisted living floor plan.
The entire building is a gabled/hip roof that is a combination of wood trusses, and part is stick framed (2x rafters and 2x ceiling joists). Currently blown-in insulation at the ceiling plane. Ceiling is (2) layers of type X gyp. bd. All interior partitions terminate at the ceiling plane (not what would happen if we were building today, but it is what it is).
At the time it was built (not certain what codes applied at the time) it was common to utilize 2-layers of 5/8" type X gyp bd fastened to the bottom of the roof framing. I've seen this approach on many assisted living facilities of that time period, it seems to have been an acceptable practice at least in several States.
The owner is looking to convert the dry sprinkler system to a wet system which will require removing all the blown-in insulation and installing open-cell spray foam insulation at the roof deck. This conversion of dry to wet and creating a tempered attic is one we've done before in different jurisdictions. Typically the AHJ has seen it as a positive improvement.
This project AHJ applicable codes are 2012 IBC and 2012 NFPA 101 Life Safety. They do not utilize the IBC existing building code.
The AHJ is requesting that we identify the UL assembly that allows there to be foam installed in the attic. So I'm trying to determine how to approach this. This AHJ is historically sticklers for requiring that the identified UL assembly be followed to the letter - for example, if the assembly doesn't specifically say National Gypsum, you will have a problem at inspection.
The existing construction does not fit nice and neat into a UL roof/ceiling assembly.
The specific items are:
No UL assembly includes (2) layers of 5/8" type X at the ceiling plane - they all are steel channels with (1) layer of 5/8" typically type C
No UL assembly includes the option for non-truss roof construction.
No UL assembly includes the specific spray foam that the contractor is planning on utilizing (we can work on this one
)
Has anyone had a similar situation? And what approach did you take?
The entire building is a gabled/hip roof that is a combination of wood trusses, and part is stick framed (2x rafters and 2x ceiling joists). Currently blown-in insulation at the ceiling plane. Ceiling is (2) layers of type X gyp. bd. All interior partitions terminate at the ceiling plane (not what would happen if we were building today, but it is what it is).
At the time it was built (not certain what codes applied at the time) it was common to utilize 2-layers of 5/8" type X gyp bd fastened to the bottom of the roof framing. I've seen this approach on many assisted living facilities of that time period, it seems to have been an acceptable practice at least in several States.
The owner is looking to convert the dry sprinkler system to a wet system which will require removing all the blown-in insulation and installing open-cell spray foam insulation at the roof deck. This conversion of dry to wet and creating a tempered attic is one we've done before in different jurisdictions. Typically the AHJ has seen it as a positive improvement.
This project AHJ applicable codes are 2012 IBC and 2012 NFPA 101 Life Safety. They do not utilize the IBC existing building code.
The AHJ is requesting that we identify the UL assembly that allows there to be foam installed in the attic. So I'm trying to determine how to approach this. This AHJ is historically sticklers for requiring that the identified UL assembly be followed to the letter - for example, if the assembly doesn't specifically say National Gypsum, you will have a problem at inspection.
The existing construction does not fit nice and neat into a UL roof/ceiling assembly.
The specific items are:
No UL assembly includes (2) layers of 5/8" type X at the ceiling plane - they all are steel channels with (1) layer of 5/8" typically type C
No UL assembly includes the option for non-truss roof construction.
No UL assembly includes the specific spray foam that the contractor is planning on utilizing (we can work on this one

Has anyone had a similar situation? And what approach did you take?