So, I'm familiar with the IBC, though I've been doing residential work for some time and I'm a bit rusty. I have no experience with the International Existing Building Code, and I didn't consider that until just now, so if I should be using it, please advise. My question has to do with how to approach an alteration to an existing building, for which the AHJ is requesting an "overall building analysis to show that heights/areas and life safety codes are being met or maintained." The building is an existing , non-sprinklered, one-story, with basement:
The local code is 2009 IBC.
We are essentially adding two exterior walls to enclose approximately 4,500 SF of the covered storage area (think carport) to create an S-1 garage space. See the attached plan (hopefully it will work!)
https://imgur.com/a/WIeC6K5
I first thought I should do non-separated and found that the more restrictive S-1 limit is 17,500 SF per floor. Since our entire footprint has >20' access, 1.5X area allowable gives me 17,500 x 1.5=26,250 SF. We will be under this amount.
Because we are trying to avoid adding sprinklers, I need to keep the S-1 Fire Areas under 5,000, which is easily accomplished since the existing exterior walls are 12" CMU. All we planned to do is replace existing doors with 3-hour doors, since the 12" CMU provides at least 3-hour separation.
Once I got to this point, I realized that this enclosed area can be considered a separate building, but I don't know how to complete the standard code analysis block that I am referring to in either of the two above scenarios. Or at least until I'm confident of the right way to approach this project, code-wise. I also keep coming back to the fact that we technically are not increasing the area of the building (since IBC considered the covered portion part of the building area).
The code "block" from the previous addition to this building, which I'm using for reference, includes:
- Basement: 9,133 SF
- First Level: 16,163 SF
- Covered Storage attached to building: 7,010 SF
The local code is 2009 IBC.
We are essentially adding two exterior walls to enclose approximately 4,500 SF of the covered storage area (think carport) to create an S-1 garage space. See the attached plan (hopefully it will work!)
https://imgur.com/a/WIeC6K5
I first thought I should do non-separated and found that the more restrictive S-1 limit is 17,500 SF per floor. Since our entire footprint has >20' access, 1.5X area allowable gives me 17,500 x 1.5=26,250 SF. We will be under this amount.
Because we are trying to avoid adding sprinklers, I need to keep the S-1 Fire Areas under 5,000, which is easily accomplished since the existing exterior walls are 12" CMU. All we planned to do is replace existing doors with 3-hour doors, since the 12" CMU provides at least 3-hour separation.
Once I got to this point, I realized that this enclosed area can be considered a separate building, but I don't know how to complete the standard code analysis block that I am referring to in either of the two above scenarios. Or at least until I'm confident of the right way to approach this project, code-wise. I also keep coming back to the fact that we technically are not increasing the area of the building (since IBC considered the covered portion part of the building area).
The code "block" from the previous addition to this building, which I'm using for reference, includes:
- Codes
- Building Code Classification
- Use Group
- Construction Type
- Building Areas/Allowable Areas, including increases
- Occupant Loads
- Max. Travel Distance
- Exit Locations
- Dead End limits
- Storage Area separations
- Plumbing Fixture Counts (not on the referenced block, but in other examples)