mtlogcabin
SAWHORSE
This has been quite interesting to follow and has usual brudgers comments can make us think and dive deep into our thought process. Sometimes we tend to go to deep.
Here is my take
Chapter 5 controls height and area of buildings period
501.1 Scope.
The provisions of this chapter control the height and area of structures hereafter erected and additions to existing structures.
503.1.2 Buildings on same lot. Simply states you have to meet the requirements of Table 503 Sections 504 and 506
The provisions of this code applicable to the aggregate building shall be applicable to each building. Does not mean the existing building needs to meet today’s code. The existing building and the new building need to be compatible as one. A type II existing building and a Type V new building would have to be considered as a Type V building. If the existing building got a frontage increase for all 4 sides then it would have to be re-evaluated as one building. Same if the existing got an increase for sprinklers the new building would have to have sprinklers.
Same with occupancy types. The most restrictive applies to the height and area limits.
Even if you believe a new building under 503.1.2 is an addition under Chapter 34 you are only required to comply with Chapter 5
3403.1 General.
Additions to any building or structure shall comply with the requirements of this code for new construction. Alterations to the existing building or structure shall be made to ensure that the existing building or structure together with the addition are no less conforming with the provisions of this code than the existing building or structure was prior to the addition . An existing building together with its additions shall comply with the height and area provisions of Chapter 5.
Here is my take
Chapter 5 controls height and area of buildings period
501.1 Scope.
The provisions of this chapter control the height and area of structures hereafter erected and additions to existing structures.
503.1.2 Buildings on same lot. Simply states you have to meet the requirements of Table 503 Sections 504 and 506
The provisions of this code applicable to the aggregate building shall be applicable to each building. Does not mean the existing building needs to meet today’s code. The existing building and the new building need to be compatible as one. A type II existing building and a Type V new building would have to be considered as a Type V building. If the existing building got a frontage increase for all 4 sides then it would have to be re-evaluated as one building. Same if the existing got an increase for sprinklers the new building would have to have sprinklers.
Same with occupancy types. The most restrictive applies to the height and area limits.
Even if you believe a new building under 503.1.2 is an addition under Chapter 34 you are only required to comply with Chapter 5
3403.1 General.
Additions to any building or structure shall comply with the requirements of this code for new construction. Alterations to the existing building or structure shall be made to ensure that the existing building or structure together with the addition are no less conforming with the provisions of this code than the existing building or structure was prior to the addition . An existing building together with its additions shall comply with the height and area provisions of Chapter 5.