This looks like a Kohler installation. Take 6 minutes and see if you can spot any violations. If so, cite the code and section.
[video=youtube;fLjHPKkIMWo]
[video=youtube;fLjHPKkIMWo]
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Most of these backup generators have an internal OCPD that serves ad a means of disconnect. Also the transfer switch serves as a disconnect.jwelectric said:I did not see the 702.12-225.31 disconnect between the generator and the house. Is there one?
Yes, I agreeelectriclese said:Most of these backup generators have an internal OCPD that serves ad a means of disconnect. Also the transfer switch serves as a disconnect.
electriclese said:Most of these backup generators have an internal OCPD that serves ad a means of disconnect. Also the transfer switch serves as a disconnect.
2005jar546 said:Yes, I agree
An inspection in no way makes an installation compliant. Code compliance makes an installation compliant.The installation posted above is not compliant with any code I am aware of and the inspector needs a continuing education class if he passed this installation.jar546 said:This was installed in Sterling, Virginia. So I assume they require a permit and inspection for this? It is obviously a compliant installation because it must have been inspected. I guess...................
It matters the jurisdiction your in. The draft stopping and CSST bonding are the responsibility of the electrical inspector in NJ by state statutes.jwelectric said:A good case in point is the venting of a bath fan, not required by the NEC. Draft stopping, not required by the NEC. Bonding of CSST gas pipe, not required by the NEC but electrical inspectors write these up on the electrical inspections daily. Bath fan venting and CSST pipe bonding is a requirement of the Mechanical code and draft stopping is a building code issue. .
Excellent point. Many times we think that the world revolves around our neck of the woods, when in fact, many local and state rules and regulations make a significant difference.rnapier said:It matters the jurisdiction your in. The draft stopping and CSST bonding are the responsibility of the electrical inspector in NJ by state statutes.
True but my statement was clear, "not required by the NEC"In NC it would be against the law for an electrician to install the bath fan vent. The CSST bonding is a manufacture requirement that is addressed to the installer and the electrician is not the installer of the CSST pipe therefore it becomes a mechanical inspection criteria not an electrical criteria although it would be an electrical installation.rnapier said:It matters the jurisdiction your in. The draft stopping and CSST bonding are the responsibility of the electrical inspector in NJ by state statutes.
If you don't mind would you post the amendment that requires this up there as the wording might be helpful in other places.Here in NC the draft stopping is in the building code not the electrical code.rnapier said:It matters the jurisdiction your in. The draft stopping and CSST bonding are the responsibility of the electrical inspector in NJ by state statutes.
The IRC specifically has a CSST bonding requirement so it is beyond the manufacturer's requirement. The bond is done with electrical wire and connected to the electrical grounding system. As an combination inspector, I can give a crap who does it but will fail the installation and the mechanical contractor, plumber and electrician can all fight over who is going to fix it but it won't pass inspection until it is done. The semantics of it is a problem for the trades, not the inspector.jwelectric said:If you don't mind would you post the amendment that requires this up there as the wording might be helpful in other places.Here in NC the draft stopping is in the building code not the electrical code.
The CSST bonding is in the listing and labeling requirements of the CSST pipe and not in any code therefore outside the electrical inspectors rights to require it to be installed although when it is installed the electrical inspector must be the one to do the inspection.
it is a catch 22 as the heating inspector cannot require an electrical inspection even if it is a multi-trade inspector.