electriclese said:
Most of these backup generators have an internal OCPD that serves ad a means of disconnect. Also the transfer switch serves as a disconnect.
jar546 said:
2005
702.11 Outdoor Generator Sets
Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure.
2008
702.11 Outdoor Generator Sets.
Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure. The disconnecting means shall meet the requirements of 225.36.
It was moved in the 2011 cycle to 702.12 but the wording is the same as in 2008
Notice that all three cycles makes the comment that the disconnect on the generator must be within sight of the building that it serves. It doesn’t say that the generator is to be within sight but the disconnect must be within sight so if it can’t be seen then it ain’t within sight.
Also notice the requirement that the disconnect meet the requirements of 225.36 which is as follows;
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
And here is 225.31
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
If neither the disconnect on the generator or the transfer switch is suitable as service equipment then neither would meet the requirements and a disconnect is required to be installed.
In the video they installed a service disconnect which tells me the transfer switch is not suitable as service equipment.