Look at the difference between the ICC IMC and the ICC based FBC here in Florida:
Thoughts?
Exception: Smoke detectors are not required in the supply air system where all portions of the building served by the air distribution system are protected by area smoke detectors connected to a fire alarm system in accordance with the Florida Fire Prevention Code. The area smoke detection system shall comply with Section 606.4.
ICC - 2018
606.2.1 Return Air Systems
Smoke detectors shall be installed in return air systems with a design capacity greater than 2,000 cfm (0.9 m3/s), in the return air duct or plenum upstream of any filters, exhaust air connections, outdoor air connections, or decontamination equipment and appliances.
Exception: Smoke detectors are not required in the return air system where all portions of the building served by the air distribution system are protected by area smoke detectors connected to a fire alarm system in accordance with the International Fire Code. The area smoke detection system shall comply with Section 606.4.
Thoughts?
FBC - 2020
606.2.1
To prevent the recirculation of dangerous quantities of smoke, a detector approved for air duct use shall be installed on the supply side of air-handling systems as required by NFPA 90A, Standard for the Installation of Air Conditioning and Ventilating Systems. Smoke detectors listed for use in air distribution systems shall be located downstream of the air filters and ahead of any branch connections in air supply systems having the capacity greater than 2000 cubic feet per minute.Exception: Smoke detectors are not required in the supply air system where all portions of the building served by the air distribution system are protected by area smoke detectors connected to a fire alarm system in accordance with the Florida Fire Prevention Code. The area smoke detection system shall comply with Section 606.4.
ICC - 2018
606.2.1 Return Air Systems
Smoke detectors shall be installed in return air systems with a design capacity greater than 2,000 cfm (0.9 m3/s), in the return air duct or plenum upstream of any filters, exhaust air connections, outdoor air connections, or decontamination equipment and appliances.
Exception: Smoke detectors are not required in the return air system where all portions of the building served by the air distribution system are protected by area smoke detectors connected to a fire alarm system in accordance with the International Fire Code. The area smoke detection system shall comply with Section 606.4.