Hydro Testing

We require it per the NFPA 13 specifications: 20 or fewer sprinklers altered, hydrostatic test for 2 hours at normal system pressure; more than 20 sprinklers altered, hydrostatic test at 200 psi, or 50 psi above the system working pressure when the system working pressure is greater than 150 psi. (Section 25.2 in the 2013 edition of NFPA 13)
 
20 head plus, at discretion of inspector, if new larger lines have been added

it is hyrdo tested constantly anyway, unless a dry pipe system
 
We always do if over the 20 heads. I have had 2 jobs where they've used the exception about not being able to isolate sections and did not want to put pressure on the entire system, Given the age of the systems, I allowed them to not do hydro. That is permitted per NFPA 13 (2010, our currently adopted version)

24.2.1.6 Modifications that cannot be isolated, such as relocated drops, shall not require testing in excess of system working pressure.
 
Last edited by a moderator:
cda said:
Put what is system working pressure?Main pressure or FD pressure?
Yep so what happens when the FD shows up and pumps the FDC at 150 psi? That would be my working pressure I would want to see, perhaps more if a high rise bld.
 
Yes, I was actually not happy that went into 13 because it is an easy way for a lazy contractor to get out of the hydro.

Like I said, we have only allowed it twice and we used the main pressure of the riser (static). That's the definition they use and specifically say it is exclusive of FDC pressure (i guess they knew we'd say that :surr )

3.3.23 System Working Pressure. The maximum anticipated static (nonflowing) or flowing pressure applied to sprinkler system components exclusive of surge pressures and exclusive of pressure from the fire department connection.
 
This particular project was just over 20 heads and a lot of complaints about me requiring the test. Nothing new just wanted a sounding board. Good answers! The test was conducted @ 9:00am this morning all held so now not as big an issue as on Friday.
 