REGISTERED
I am trying to find the window sill height and fall protection requirements for a commercial storage area on the second floor.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Thanks, Just wanted to make sure.None....
You can still fall out a window in commercial buildings. I would definitely consider an open window next to an area people walk an "open sided walking surface" I don't know why a window would make any difference, the hazard is identical if the window is open. Maybe if the window only opened 21" it could be the guardrail. Otherwise, I'd put a bar across it at 21" & 42".I think you reaching there myself. If R-2 or R-3 you can get to 1015.8 through 1015.1, but commercial? I think not. JMHO
not reallyThere are no specific sill height and fall protection requirements for windows outside of R-2,3. However, I consider those additional requirements to 1015.2. Is there a walking surface next to the windows? Is the sill height less than 42"? IS the grade more than 30" below the window sill? If the answer is yes to all three then you need a guardrail.
I'm genuinely curious how you justify an opening in a wall (an open window) on the second story next to a walking surface would not need a guardrail.not really
I can't find any code that would require what you have outlined.I'm genuinely curious how you justify an opening in a wall (an open window) on the second story next to a walking surface would not need a guardrail.
1015.2 and common sense.I can't find any code that would require what you have outlined.
I freely admit to enforcing common sense that has a tenuous basis in code. This window that you have suggested would probably get my attention....but as Tommy, the oldest Henderson boy said, "Here's the thing about that." Instead of a guard I would ask for a wall....and that would go nowhere.1015.2 and common sense.
What if the window is 4' wide and tall with a 6" sill height? That opening doesn't need a guardrail?
This isn't even a "what if". 1015.2 requires a guard.The second you find yourself applying "what if" to the code, you are wrong....I would agree it is bad design just like a 29.5" high sidewalk, but code does not require any protection there either....
No guardrails in Canada's commercial code? Weird.Our code deals with this similarly to yours:
A window in a public area that extends to less than 1000 mm above the floor and is located above the second storey in a building of residential occupancy, shall be protected by a barrier or railing no less than 1070 mm above the floor, of the window shall be non-openable and designed to withstand the lateral design loads for balcony guards required by article 4.1.5.14.
So, if it is not a residential occupancy, no protection is required.
Oh no, we require them in any surface that is 600mm above an adjacent surface or a slope of more than 1 in 2 to within 1200mm of the walking surface.No guardrails in Canada's commercial code? Weird.
OK, make it a floor to ceiling operable window. No landing required. According to you that's no problem.Doors need landings 1010.1.6 which would then be a walking surface which would require a guard...
Yes. Wind loads would surpass the guardrail load in any case.So you call all exterior windows guards? Do you make them meet this?
1015.2.1 Glazing. Where glass is used to provide a guard
or as a portion of the guard system, the guard shall comply
with Section 2407. Where the glazing provided does
not meet the strength and attachment requirements of Section
1607.8, complying guards shall be located along
glazed sides of open-sided walking surfaces.