jar546
CBO
Wall studs of combustible wood construction with gypsum board covering that terminates above the drop ceiling but before the top plate(s) on interior and exterior walls.
There is now a gap between the end of the gypsum and the solid wood top plate that is open to the stud cavity below. This, in turn, allows any fire that starts in a wall cavity, such as an electrical fire to spread to above the drop ceiling with no barriers in place.
At the half way point of the wall, the contractor has some bracing that does not meet the requirements of draftstopping but does block the cavity about 4' off the floor. The other half is open to the drop ceiling cavity because they did not run the gypsum all the way up to the top plate(s).
We believe that IBC 717 applies, specifically this language in the IBC:
Now for a history lesson on this property that is being renovated with change of use and Level 3.
I don't have all of the particulars but here are the basics.
*The plans were initially rejected for lack of a sprinkler system being added as required.
*The RDP then added a fire barrier to break up the building to circumvent the sprinkler system
*We then stopped the job because the contractor did not follow the prints and started framing exterior walls with combustible wood which was not allowed for the type construction.
*The RDP then changed the type of construction to allow this and manipulated the fire barriers to allow it.
Now they want their cake, they want to eat it and I think they want us to serve it to them on a silver platter.
What you think?
There is now a gap between the end of the gypsum and the solid wood top plate that is open to the stud cavity below. This, in turn, allows any fire that starts in a wall cavity, such as an electrical fire to spread to above the drop ceiling with no barriers in place.
At the half way point of the wall, the contractor has some bracing that does not meet the requirements of draftstopping but does block the cavity about 4' off the floor. The other half is open to the drop ceiling cavity because they did not run the gypsum all the way up to the top plate(s).
We believe that IBC 717 applies, specifically this language in the IBC:
Neither the contractor nor the RDP agree with this.717.2.3 Connections between horizontal and verticalspaces. Fireblocking shall be provided at interconnections
between concealed vertical stud wall or partition spaces and
concealed horizontal spaces created by an assembly of floor
joists or trusses, and between concealed vertical and horizontal
spaces such as occur at soffits, drop ceilings, cove
ceilings and similar locations.
Now for a history lesson on this property that is being renovated with change of use and Level 3.
I don't have all of the particulars but here are the basics.
*The plans were initially rejected for lack of a sprinkler system being added as required.
*The RDP then added a fire barrier to break up the building to circumvent the sprinkler system
*We then stopped the job because the contractor did not follow the prints and started framing exterior walls with combustible wood which was not allowed for the type construction.
*The RDP then changed the type of construction to allow this and manipulated the fire barriers to allow it.
Now they want their cake, they want to eat it and I think they want us to serve it to them on a silver platter.
What you think?