• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

IBC Fire Areas

NFJ

Registered User
Joined
Jun 30, 2022
Messages
3
Location
United States
Hello - Curious if the NFPA 101 has requirements similar to FIRE AREAS in the IBC? We are working on a project that contains a vehicle repair shop, and need to know if NFPA has area and fire barrier limitations similar to the IBC. Trying to avoid fire sprinkler requirement.
 
The fire area is a building construction concept that allows the use of passive fire protection (i.e., fire-rated construction) instead of active fire protection (i.e., fire sprinklers). Its primary purpose is the protection of the structure and life safety is secondary. The NFPA 101 is focused primarily on life safety with a heavy emphasis on means of egress. It is not intended to be a building code--that is where the NFPA 5000 comes in.

NFPA 101 does not provide a definition for fire area, but NFPA 5000 does, which gives you an idea if a term is used within an NFPA code or standard. NFPA will define all applicable terms used within a code or standard in that code or standard. Unlike the NFPA, ICC states that terms not defined within a code but defined in other codes will have the same meaning as those defined in other codes.
 