Hi All,
Long time viewer, first time poster. I'm working on a small commercial project and running into a disagreement with the Fire Marshall regarding required Fire Separations in a multiple occupancy building. I mostly do residential work so appreciate everyone's experience on this.
From what I can tell, there is a contradiction between the IBC and NFPA regarding rules for nonseparated multiple occupancy buildings. IBC 2018 508.3 'Nonseparated Occupancies' provides some leeway for buildings with multiple occupancies. It states that you can have a building with multiple unseparated occupancies as long as you apply code requirements for each space per the occupancy classification of the space and that the most restrictive provisions of Chapter 9 (Fire Protection and Life Safety) for each occupancy apply to the whole building. Some high hazard occupancies and Residential separation requirements still apply. This makes a lot of sense to me. There are many small buildings with multiple occupancy types where the small size of the building negate any realistic dangers to life safety from having these occupancies next to each other without separation.
NFPA 101 2021 (applicable code on the project) seems to have a similar section but upon detailed reading (And my FM's interpretation) it appears to be much more restrictive in a way that (to me) does not make sense. Section 6.1.14 provides for 'Multiple Occupancies'. It categorizes 'Multiple Occupancies' as either being 'Mixed Occupancies' or 'Separated Occupancies' and also includes provisions for incidental occupancies (appears to be similar to 'Accessory Occupancies' in the IBC). Per section 6.1.14.3 'Mixed Occupancies' appear to be similar to 'Nonseparated Occupancies' in the IBC as it includes the requirement for the most restrictive requirements of each occupancy to apply for the whole building. However, in section 6.1.14.1.2 it states that "Where exit access from an occupancy traverses another occupancy, the multiple occupancy shall be treated as a mixed occupancy". This indicates that nonseparated occupancies are only allowed in buildings where the different occupancies are mixed together with a shared tenant/owner (The example given by the FM was a School).
Do you all agree with this code interpretation? If so is this just a contradiction between the codes? The 'nonseparated occupancies' provision in the IBC seems to give leeway in many situations where the NFPA would require fire separation.
It also seems to me that the NFPA requirements don't make sense. For example, if I had a 1 story, 1,000 sf building and had half of it office and half mercantile with each space having a separate exit then I'd have to provide fire separation between the spaces. However, if I have the office portion egressing through the mercantile portion and sharing a single exit then fire separation isn't required. This second condition reduces the number of exits in the building and overall safety yet doesn't require fire separation. Nevermind that such a small building is not really a danger from an egressing perspective and fire separation is not a significant life safety concern.
Long time viewer, first time poster. I'm working on a small commercial project and running into a disagreement with the Fire Marshall regarding required Fire Separations in a multiple occupancy building. I mostly do residential work so appreciate everyone's experience on this.
From what I can tell, there is a contradiction between the IBC and NFPA regarding rules for nonseparated multiple occupancy buildings. IBC 2018 508.3 'Nonseparated Occupancies' provides some leeway for buildings with multiple occupancies. It states that you can have a building with multiple unseparated occupancies as long as you apply code requirements for each space per the occupancy classification of the space and that the most restrictive provisions of Chapter 9 (Fire Protection and Life Safety) for each occupancy apply to the whole building. Some high hazard occupancies and Residential separation requirements still apply. This makes a lot of sense to me. There are many small buildings with multiple occupancy types where the small size of the building negate any realistic dangers to life safety from having these occupancies next to each other without separation.
NFPA 101 2021 (applicable code on the project) seems to have a similar section but upon detailed reading (And my FM's interpretation) it appears to be much more restrictive in a way that (to me) does not make sense. Section 6.1.14 provides for 'Multiple Occupancies'. It categorizes 'Multiple Occupancies' as either being 'Mixed Occupancies' or 'Separated Occupancies' and also includes provisions for incidental occupancies (appears to be similar to 'Accessory Occupancies' in the IBC). Per section 6.1.14.3 'Mixed Occupancies' appear to be similar to 'Nonseparated Occupancies' in the IBC as it includes the requirement for the most restrictive requirements of each occupancy to apply for the whole building. However, in section 6.1.14.1.2 it states that "Where exit access from an occupancy traverses another occupancy, the multiple occupancy shall be treated as a mixed occupancy". This indicates that nonseparated occupancies are only allowed in buildings where the different occupancies are mixed together with a shared tenant/owner (The example given by the FM was a School).
Do you all agree with this code interpretation? If so is this just a contradiction between the codes? The 'nonseparated occupancies' provision in the IBC seems to give leeway in many situations where the NFPA would require fire separation.
It also seems to me that the NFPA requirements don't make sense. For example, if I had a 1 story, 1,000 sf building and had half of it office and half mercantile with each space having a separate exit then I'd have to provide fire separation between the spaces. However, if I have the office portion egressing through the mercantile portion and sharing a single exit then fire separation isn't required. This second condition reduces the number of exits in the building and overall safety yet doesn't require fire separation. Nevermind that such a small building is not really a danger from an egressing perspective and fire separation is not a significant life safety concern.