The 2009 IBC requires a curtainwall to provide perimeter fire containment where there is a fire resistance-rated floor or floor ceiling assembly is required. I have sent an Engineering Judgement to UL and they responded with the assemblies that meet the requirements and, essentially, they fall into two categories; those that are 6" from the top of the slab and those that range between 24-inches and 34-inches depending on the size of the spandrel panel. They were also very specific that for an assembly to meet ASTM E119 it must indicate both an Integrity rating and a Insulation rating. Those indicating F and T ratings only comply with ASTM E814. Yet I continue to see high-rise after high-rise being constructed with the glass going to the slab. Am I missing something?