Old terminology would have been Type I = Fire resistive and Type II = Non-combustible.
The required ratings based on Construction Type are in Table 601 (below, don't forget to check applicable footnotes...).
The base line for most elements in Type IB is 2 hours, which includes most load bearing elements. The steel columns, lacking any specific protection, will likely land you in Type IIB. You did not indicate if the 1 hour partitions are load bearing (partitions generally aren't). Your two basic options are:
1 - Classify it and let the design professional justify a different classification, or
2 - Ask the DP to identify the ratings for critical areas identified in the Code and the table.
[TD=width: 32%, align: center]
BUILDING ELEMENT
[/TD]
[TD=colspan: 2, align: center]
TYPE I
[/TD]
[TD=colspan: 2, align: center]
TYPE II
[/TD]
[TD=colspan: 2, align: center]
TYPE III
[/TD]
[TD=width: 7%, align: center]
TYPE IV
[/TD]
[TD=colspan: 2, align: center]
TYPE V
[/TD]
[TD=width: 9%, align: center]
A
[/TD]
[TD=width: 8%, align: center]
B
[/TD]
[TD=width: 8%, align: center]
A
d
[/TD]
[TD=width: 6%, align: center]
B
[/TD]
[TD=width: 8%, align: center]
A
d
[/TD]
[TD=width: 6%, align: center]
B
[/TD]
[TD=align: center]
HT
[/TD]
[TD=width: 6%, align: center]
A
d
[/TD]
[TD=width: 5%, align: center]
B
[/TD]
[TD=align: left]Primary structural frame
g
(see Section 202 ) [/TD]
[TD=align: center]3
a
[/TD]
[TD=align: center]2
a
[/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]HT [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: left]Bearing walls [/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: center][/TD]
[TD=align: left] Exterior
f, g
[/TD]
[TD=align: center]3 [/TD]
[TD=align: center]2 [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]2 [/TD]
[TD=align: center]2 [/TD]
[TD=align: center]2 [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: left] Interior [/TD]
[TD=align: center]3
a
[/TD]
[TD=align: center]2
a
[/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]1/HT [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: left]Nonbearing walls and partitions
Exterior [/TD]
[TD=colspan: 9, align: center]See Table 602 [/TD]
[TD=align: left]Nonbearing walls and partitions
Interior
e
[/TD]
[TD=align: center]0 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]See Section 602.4.6 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]0 [/TD]
[TD=align: left]Floor construction and associated secondary member
(see Section 202 ) [/TD]
[TD=align: center]2 [/TD]
[TD=align: center]2 [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: center]HT [/TD]
[TD=align: center]1 [/TD]
[TD=align: center]0 [/TD]
[TD=align: left]Roof construction and associated secondary members
(see Section 202 ) [/TD]
[TD=align: center]1
1
/
2
b
[/TD]
[TD=align: center]1
b,c
[/TD]
[TD=align: center]1
b,c
[/TD]
[TD=align: center]0
c
[/TD]
[TD=align: center]1
b,c
[/TD]
[TD=align: center]0 [/TD]
[TD=align: center]HT [/TD]
[TD=align: center]1
b,c
[/TD]
[TD=align: center]0 [/TD]
602.2 Types I and II.
Types I and II construction are those types of construction in which the building elements listed in Table 601 are of noncombustible materials, except as permitted in Section 603 and elsewhere in this code.