I have another question concerning accessibility - an on site inspection by a state ran agency has stated the following code section in regards to a Men's group restroom with two urinals. Alcove - ICC ANSI 305.7


upload_2018-1-22_19-14-21.png

The inspection has identified the following restroom as being non-compliant.

upload_2018-1-22_19-19-36.png

If this is the case, why would you ever replace a water closet with an Urinal?

Have any of you ever been cited for this application of an Alcove as outlined in ICC ANSI Clear Floor
 

Attachments

  • upload_2018-1-22_19-16-27.png
    upload_2018-1-22_19-16-27.png
    127.7 KB · Views: 5
I have cited that section where the urinal screen is >24".......Also on drinking fountains and lavs....305.7.2 is required at the urinal as I don't believe you can do parallel on that one...
 
based on the drawing there is not 18" clear at the screen. The screen appears to be inside the clear area.
 
The issue at hand is the standard floor plan is for 30" face to face of partition walls..... according to the ICC Ansi alcove, it states teh following:

upload_2018-1-24_21-59-36.png
The item of discussion is the fact that the urinal partition is not over 24" in depth, therefore the alcove created by the partitions is not deeper than 24" in depth.
 

Attachments

  • upload_2018-1-24_22-0-59.png
    upload_2018-1-24_22-0-59.png
    28.3 KB · Views: 1
That may be the "minimum" but in practice it is not "best practice" to do so as it leaves no room for less than perpendicular approach.
If a number of side by side with waterless urinals, note the floor below the urinals or your shoes (smiling).
 
While we are here....If only one side is greater than 24" and one less, does it still apply? Is that what the "on all or part of three sides" comes from or means?
 
There you go, splitting hairs; if the wall on the left is the room wall >24" then 18" applies, if on the right is <24" that side can be 15".
 
Interesting, interpretation from ADA Access Board

As noted in the disclaimer below, this is informal assistance. We do not enforce the Americans with Disabilities Act (ADA), nor do we interpret ANSI A117.9.


In terms of the ADA and the 2010 ADA Standards, in our online guide, on Chapter 3: Building Blocks, Clear Floor or Ground Space …, we say in the section titled Approach and Maneuvering Clearance [§305.6 and §305.7]: Where the space is obstructed on both sides for more than half the depth, additional clearance is required for maneuvering. Accessible routes must connect to the unobstructed side of the space.


Since both sides of your 30” by 48” are not obstructed more than 24”, the width is not required to be increased to 36”.


Link to online guides: https://www.access-board.gov/guidel...-the-ada-standards/guide-to-the-ada-standards

Link to combined ADA Standards (including the 2010): https://www.access-board.gov/guidel...d-sites/about-the-ada-standards/ada-standards


Paul Beatty


Disclaimer: Technical assistance provided in this email is intended solely as informal guidance; it is neither a determination of your legal rights or responsibilities, nor a statement of the official views of the U.S. Access Board or any other federal agency. Any links to non-federal websites are provided as a courtesy and do not represent an endorsement of the linked information, products, or services.
 