Given:
Existing 94,016sf one story office building. Type IIIB Fully Sprinkled. Currently divided into 2 tenant spaces.
Former tenant of one of the spaces electively installed a fire alarm system including smoke/ducts, horn/strobes, and annunciator that covered their space only in order to comply with their corporate risk management policies since most of their facilities were educational in nature. This office was a straight business occupancy in an existing building with smaller package heat pumps. As such, they were not required by the IFC to have or install a fire alarm system, only flow tamper with dialer for the sprinkler system, which was existing. IFC Section 907.9 refers to Table 1103.1 where existing buildings with Group B occupancies are exempt. That tenant has since filed BK and vacated the building.
New tenant for this space moves in. Same occupancy class. Because the alarm system has been problematic from a maintenance standpoint, the building ownership wants to remove the fire alarm system that was originally installed electively, leaving only the required sprinkler flow to dialer system.
While the IFC seems to exempt the requirement, IEBC Section 703.1 requires that any alteration shall be done in a manner that maintains the level of fire protection provided. Some municipalities, like Longmont, Colorado, for instance, have amended the IEBC to change the word "Provided" with the word "Required", thereby theoretically allowing removal in our case since it is and was not "required"
QUESTION: Curious on how many of you have seen similar amendments out there? Was "required" a more appropriate word than "provided" with the original intent? Don't have a copy of the commentary, so not sure if that's part of the discussion there or not?
We're being told that IEBC 703.1, is the overriding piece of code and therefore, the existing fire alarm system must remain in place.
Existing 94,016sf one story office building. Type IIIB Fully Sprinkled. Currently divided into 2 tenant spaces.
Former tenant of one of the spaces electively installed a fire alarm system including smoke/ducts, horn/strobes, and annunciator that covered their space only in order to comply with their corporate risk management policies since most of their facilities were educational in nature. This office was a straight business occupancy in an existing building with smaller package heat pumps. As such, they were not required by the IFC to have or install a fire alarm system, only flow tamper with dialer for the sprinkler system, which was existing. IFC Section 907.9 refers to Table 1103.1 where existing buildings with Group B occupancies are exempt. That tenant has since filed BK and vacated the building.
New tenant for this space moves in. Same occupancy class. Because the alarm system has been problematic from a maintenance standpoint, the building ownership wants to remove the fire alarm system that was originally installed electively, leaving only the required sprinkler flow to dialer system.
While the IFC seems to exempt the requirement, IEBC Section 703.1 requires that any alteration shall be done in a manner that maintains the level of fire protection provided. Some municipalities, like Longmont, Colorado, for instance, have amended the IEBC to change the word "Provided" with the word "Required", thereby theoretically allowing removal in our case since it is and was not "required"
QUESTION: Curious on how many of you have seen similar amendments out there? Was "required" a more appropriate word than "provided" with the original intent? Don't have a copy of the commentary, so not sure if that's part of the discussion there or not?
We're being told that IEBC 703.1, is the overriding piece of code and therefore, the existing fire alarm system must remain in place.