This is a long post, and probably am leaving some information out.
This is the 3rd job I have done with the inspector in the last year.
My problem is he does not seem to know the codes, nor enforce the codes the same to all parties. He holds the contractor to a higher standard than those not in the trades. The last job, just finished, was in a commercial kitchen with problems with the exhaust system. There was a fire in the restuarnt, several years ago. The insurance company paid to have a new exhaust system, and suppression system installed. I did the suppression system install and passed an inspection. More importantly, it was installed to mfg requirements. The hood system was not installed to the code at that time, but passed inspection anyway. At that time, I was ignorant of any exhaust codes.
Forward to March of this year, when a new operator was interested in moving her restruant into the building. The B/O asked the State FM to inspect the exhaust system.
The main hood was OK. The main duct and 3 other ducts were made of less than 16 gauge, rivited, none of the ducts were welded or brazed, but soldered and siliconed. The sidewall fan is not listed for the application, and the clearances to combustables were unknown. I have a copy of hte FM report, and the FM required the ducts to be removed, along with the small hoods.
I also have the report from the local B/O, referring to: 1. "Per reccomendations from the State of Or Deputy Fire Marshall..........." 2. "This building department is requesting the the non-compliant ductgwork removed and new min 16 gauge stell and joints, seams and penetrations of grease ductwork welded-brazed Section 506.3.1.1 2010 OMSC."
Based upon the reports, my sheet metal man & I put together a proposal to remove all the ducts, 2 of the hoods, cap off the duct opening for the hood left in place, build a new vertical duct, remove the horizontal duct going through hte wall and use listed insulation, and use a listed access panel for cleaning purposes. We did not get the job. What was done was replace the center duct, make an access panel using a silicone sealer and use sheet metal screws to hold the panel in place. The other ducts were cut, not removed and the hoods were left in place. The job passed inspection! Of course hte inspector asked the business owner to remove the ducts, and hoods. I finished my fire system, and got paid this AM. the hoods and ducts are still in place.
I am really dissappointed in the inspector, he has inspected 5 of my jobs to date, and is usually late, or has shown up at all. This is a small office, and I am aware my specialty of fire stuff is not common. But, I expect to see myself and my competitors following the same standard. That does not happen, on this job, particulary on hte exhaust system, standards changed 3 times. I am at a loss on how to deal with this person. Other contractors have also told me of their problems with this guy and they are similar to my experience. I have suggested going to the City Mgr, but no one else wants to do that, saying they have to work with the inspector on a regular basis.
I have pictures taken to protect my company should the place catch fire. My fire system will not control a fire execpt in the main hood. I also removed the fire system from the other hoods at the direction of the inspector. If I knew how, I could post the pictures and the inspection reports, with the names and address crossed off. If I knew how.
This is the 3rd job I have done with the inspector in the last year.
My problem is he does not seem to know the codes, nor enforce the codes the same to all parties. He holds the contractor to a higher standard than those not in the trades. The last job, just finished, was in a commercial kitchen with problems with the exhaust system. There was a fire in the restuarnt, several years ago. The insurance company paid to have a new exhaust system, and suppression system installed. I did the suppression system install and passed an inspection. More importantly, it was installed to mfg requirements. The hood system was not installed to the code at that time, but passed inspection anyway. At that time, I was ignorant of any exhaust codes.
Forward to March of this year, when a new operator was interested in moving her restruant into the building. The B/O asked the State FM to inspect the exhaust system.
The main hood was OK. The main duct and 3 other ducts were made of less than 16 gauge, rivited, none of the ducts were welded or brazed, but soldered and siliconed. The sidewall fan is not listed for the application, and the clearances to combustables were unknown. I have a copy of hte FM report, and the FM required the ducts to be removed, along with the small hoods.
I also have the report from the local B/O, referring to: 1. "Per reccomendations from the State of Or Deputy Fire Marshall..........." 2. "This building department is requesting the the non-compliant ductgwork removed and new min 16 gauge stell and joints, seams and penetrations of grease ductwork welded-brazed Section 506.3.1.1 2010 OMSC."
Based upon the reports, my sheet metal man & I put together a proposal to remove all the ducts, 2 of the hoods, cap off the duct opening for the hood left in place, build a new vertical duct, remove the horizontal duct going through hte wall and use listed insulation, and use a listed access panel for cleaning purposes. We did not get the job. What was done was replace the center duct, make an access panel using a silicone sealer and use sheet metal screws to hold the panel in place. The other ducts were cut, not removed and the hoods were left in place. The job passed inspection! Of course hte inspector asked the business owner to remove the ducts, and hoods. I finished my fire system, and got paid this AM. the hoods and ducts are still in place.
I am really dissappointed in the inspector, he has inspected 5 of my jobs to date, and is usually late, or has shown up at all. This is a small office, and I am aware my specialty of fire stuff is not common. But, I expect to see myself and my competitors following the same standard. That does not happen, on this job, particulary on hte exhaust system, standards changed 3 times. I am at a loss on how to deal with this person. Other contractors have also told me of their problems with this guy and they are similar to my experience. I have suggested going to the City Mgr, but no one else wants to do that, saying they have to work with the inspector on a regular basis.
I have pictures taken to protect my company should the place catch fire. My fire system will not control a fire execpt in the main hood. I also removed the fire system from the other hoods at the direction of the inspector. If I knew how, I could post the pictures and the inspection reports, with the names and address crossed off. If I knew how.