I have a small project where a single, CAT 6, fiber cable will be
installed from one Server Room in a bldg. in to another Server
Room, ...in a Return Air Plenum.........The single cable will pass
thru a fire rated wall assembly.........I will write an Amendment
to the original Scope of Work, to require that all "thru penetrations"
in a fire rated assembly must be sealed with an approved sealant.
The fire rated wall assembly is in a corridor......The building is
fully sprinkled.
The building owner will not allow this cable to be laid upon
the ceiling grid, but rather, ...has specified that the cable must
be attached to the bldg. structural steel or to the ceiling grid
wires that the support the grid [ i.e. - according to the NEC ].
I support this decision, but will need to be able reference
the correct NEC Articles when the contractor questions the
requirement.
Q1): What NEC Article or Articles require the fiber cable to
be attached to the building's structural steel, or will allow
the attachment to the ceiling grid suspension wires ?
The 2020 and \ or the 2023 NEC is the Code being used.
Q2): Do you have any input on the sealing of the "thru
penetration" other than sealing it on both sides of the
assembly ?
As always, any input will be appreciated !
$ ~ $
I have a small project where a single, CAT 6, fiber cable will be
installed from one Server Room in a bldg. in to another Server
Room, ...in a Return Air Plenum.........The single cable will pass
thru a fire rated wall assembly.........I will write an Amendment
to the original Scope of Work, to require that all "thru penetrations"
in a fire rated assembly must be sealed with an approved sealant.
The fire rated wall assembly is in a corridor......The building is
fully sprinkled.
The building owner will not allow this cable to be laid upon
the ceiling grid, but rather, ...has specified that the cable must
be attached to the bldg. structural steel or to the ceiling grid
wires that the support the grid [ i.e. - according to the NEC ].
I support this decision, but will need to be able reference
the correct NEC Articles when the contractor questions the
requirement.
Q1): What NEC Article or Articles require the fiber cable to
be attached to the building's structural steel, or will allow
the attachment to the ceiling grid suspension wires ?
The 2020 and \ or the 2023 NEC is the Code being used.
Q2): Do you have any input on the sealing of the "thru
penetration" other than sealing it on both sides of the
assembly ?
As always, any input will be appreciated !
$ ~ $