• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Insulation question

VERMA071

Member
Joined
Apr 24, 2014
Messages
22
Location
new jersey, usa
Hello everyone,

we recently have a situation in our office where a contractor was advised to use Batt insulation (R-15) and rigid insulation (R-4) on an exterior 4" stud exterior wall.
Instead of having an OSB/ Plywood sheathing as a rigid board attached on the outside of the studs, contractor cut that rigid board and added that inside the stud bays. this has reduced the depth required for the insulation and thereby compromised the r-value of insulation. Is there any way to correct this situation from inside as exterior is already finished? we advised him to add 2x2 on the inside in front of 2x4 but he is saying it will create further issues for plumbing and electrical work. Any advice?
Thank you.
 
Per your energy code, what is the required insulation value? I am guessing that it is probably R-21 w/ intermediate framing?

Suggest that you contact the local AHJ on this one...
 
Per your energy code, what is the required insulation value? I am guessing that it is probably R-21 w/ intermediate framing?

Suggest that you contact the local AHJ on this one...
Its R-19 for the wall. AHJ is asking a letter from Architect saying R-value is not going to be reduced but we think that by compressing the insulation to accommodate in the studs, its R-value will be affected.
 
Its R-19 for the wall. AHJ is asking a letter from Architect saying R-value is not going to be reduced but we think that by compressing the insulation to accommodate in the studs, its R-value will be affected.
You are correct, the R-value will be reduced.
 
A complete ASHRAE report not just a letter from the architect should be required by the AHJ

N1101.3 (R101.5.1) Compliance materials.
The building official shall be permitted to approve specific computer software, worksheets, compliance manuals and other similar materials that meet the intent of this chapter.
 
Instead of having an OSB/ Plywood sheathing as a rigid board attached on the outside of the studs, contractor cut that rigid board and added that inside the stud bays.
I think you need to evaluate the installation of the sheathing. It’s supposed to span across multiple studs to provide racking resistance, sounds like the way he installed it … it’s not performing that function.
 
Hello everyone,

we recently have a situation in our office where a contractor was advised to use Batt insulation (R-15) and rigid insulation (R-4) on an exterior 4" stud exterior wall.
Instead of having an OSB/ Plywood sheathing as a rigid board attached on the outside of the studs, contractor cut that rigid board and added that inside the stud bays. this has reduced the depth required for the insulation and thereby compromised the r-value of insulation. Is there any way to correct this situation from inside as exterior is already finished? we advised him to add 2x2 on the inside in front of 2x4 but he is saying it will create further issues for plumbing and electrical work. Any advice?
Thank you.

It sure will create issues with the plumbing and electrical, but without removing the exterior siding and installing the rigid insulation the way he was directed, I don't see another solution.

We'll maybe some form of performance option.
 
Maybe a higher quality batt that is meant to fit a 3" space and still provide the minimum R value? Does it exist? I don't know, I suspect you could get there with rockwool
 
The insulation was supposed to span over the stud to eliminate a thermal bridge. Now the 1/2" insulation is in the stud bay......The lost depth in the stud bay for the batt insulation is negligible. So you might be getting R18 instead of R19.
 
First, verify exterior sheathing is in place, whatever the AHJ approved or will approve.

Fix 1. Pull the material out of the bays and spray foam.

Fix 2. Pull the foam board out of the bay, place your cavity insulation, R15 or whatever it is, use unfaced insulation. Then place the foam board over the face of the interior studs and tape all seams with approved tape. Finally wallboard with extended fasteners. Use electrical box extensions or adjust boxes up front. Plumbing can remain untouched, electrical, minor adjustment.

No matter which route, you’ll need AHJ approval....
 
The insulation was supposed to span over the stud to eliminate a thermal bridge. Now the 1/2" insulation is in the stud bay......The lost depth in the stud bay for the batt insulation is negligible. So you might be getting R18 instead of R19.
I believe what was built was 2x4 studs with the 1/2" osb or ply sheathing somehow inset between studs and 1" (?) R4 foam continuous across studs. I think the wall bracing has to be addressed but 1/2" R2 foam on inside should safely get the R19, better because it's continuous on both sides.
 
$ ~ $ ~ $

VERMA071,


Have you considered Cellulose Fiber Insulation ( CFI )

being blown in to the wall cavities , and afterwards,
...covering the walls with some type of plastic air barrier ?

1639554410489.png

$ ~ $ ~ $
 
If continuous insulation is not required, then it could work...The insulation manufacturers sometimes have a table of "compressed" values...

1639572619957.png

You might get there with a slightly reduced value if you run it through Res-check....The most OC says you can squish there R15 is to 2.5" and you get R11
 
If metal studs, then Ice is correct in that the thermal bridging is an issue if the insulation is not on the exterior.
 