• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Insulation Replacement in a Re-Roof C503

Hyrax4978

Registered User
Joined
Nov 28, 2016
Messages
205
Location
Hartford, CT
C503.1 is fairly self explanatory. As is exemption 4 for not exposing the cavity.
My question is in regards to exemption 3. If you expose a cavity, and there is "some" insulation. Not completely filled. Do you need to upgrade.
Its a generic question, but my specific instance is a butler roof assembly that has the draped insulation. so once you take the roof off you run into the insulation draped over the purlins. But it does not meet the current thermal requirements. to reinsulate that space is an extreme undertaking as you would now need a full liner system and filled cavity. going over the roof with EPDM and polyiso is very expensive in lieu of just replacing the metal panels. Would be nice to take the roof panel off, and just put a new on on, without touching the draped insulation.

Any thoughts....
 
Could this be considered a roof recover so exception 5 could apply?

C503.3.1 only applies to roof replacements where insulation is entirely above the roof deck.

The building manufacturer might make a system with thicker insulation and styrofoam blocks above the purlins to preevent thermal bridging.

Most metal buildings aren't engineered to take more than 1 or 2 PSF added roof load.
 