Interesting question posted by electrician

Joined
Oct 24, 2009
Messages
1,552
Location
Miami Fla
From MH's forum;

It has been suggested that the elevator shutdown due to sprinkler operation in the shaft or machine room should be delayed until the passengers are unloaded (after recall). It make sense but I can not actually find a code reference. As far as I can find, operation of sprinkler in the shaft or machine room requires that power be shut off (e.g. via shunt trip circuit breaker).Any insights?
 
also check nfpa 13 if the shaft and elevator meet certain criteria, the sprinkler at the top of the shaft is not required, eliminating need for shunt trip

what I have seen, if a sprinkler head is at the top, heat detector with smoke detector next to it. smoke does recall, prior to heat tripping the shunt trip

believe the shunt trip requirement comes from the ansi elevator stuff
 
Last edited by a moderator:
jar546 said:
Thanks Mark. I was relaxing, just checking on the forum when I saw this. Now I have work to do with all of that reading!
Glad I could make a difference in your day off

It is hard to cut and paste with the phone
 
nfpa 13 2013

8.15.5 Elevator Hoistways and Machine Rooms.

8.15.5.1* Sidewall spray sprinklers shall be installed at the bottom of each elevator hoistway not more than 2 ft (0.61 m) above the floor of the pit.

8.15.5.2 The sprinkler required at the bottom of the elevator hoistway by 8.15.5.1 shall not be required for enclosed, noncombustible elevator shafts that do not contain combustible hydraulic fluids.

8.15.5.3 Automatic fire sprinklers shall not be required in elevator machine rooms, elevator machinery spaces, control spaces, or hoistways of traction elevators installed in accordance with the applicable provisions in NFPA 101, or the applicable building code, where all of the following conditions are met:

(1)

The elevator machine room, machinery space, control room, control space, or hoistway of traction elevator is dedicated to elevator equipment only.

(2)

The elevator machine room, machine room, machinery space, control room, control space, or hoistway of traction elevators are protected by smoke detectors, or other automatic fire detection, installed in accordance with NFPA 72.

(3)

The elevator machinery space, control room, control space, or hoistway of traction elevators is separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire resistance rating of not less than that specified by the applicable building code.

(4)

No materials unrelated to elevator equipment are permitted to be stored in elevator machine rooms, machinery spaces, control rooms, control spaces, or hoistways of traction elevators.

(5)

The elevator machinery is not of the hydraulic type.

8.15.5.4* Automatic sprinklers in elevator machine rooms or at the tops of hoistways shall be of ordinary- or intermediate-temperature rating.

8.15.5.5* Upright, pendent, or sidewall spray sprinklers shall be installed at the top of elevator hoistways.

8.15.5.6 The sprinkler required at the top of the elevator hoistway by 8.15.5.5 shall not be required where the hoistway for passenger elevators is noncombustible or limited-combustible and the car enclosure materials meet the requirements of ASME A17.1, Safety Code for Elevators and Escalators.
 