Glennman CBO
Silver Member
- Joined
- Oct 20, 2009
- Messages
- 441
2009 IBC, E occupancy. Stairs that are overkill on width.
These are approximately 17 ft wide exterior stairs. They follow grade, so guards are not an issue. Required width is 140" based on occupant load.
Handrails are situated as follows, from one side to the other. 30" to the first handrail from the side, approximately 6 ft to the center handrail, then 6 ft to the next handrail, and 30" again to the opposite side. 3 handrails total.
No handrails on the "sides", as the person using the stairs on either side would have a handrail on one side of them, and the edge of the stairs on the other side of them.
They have 180" of width that is within 30" of a handrail.
Code states handrails are required on both sides of stairs. It would appear that they meet the intermediate handrail requirements of 1012.9, but not the requirement for handrails on both sides, per 1009.12.
Any thoughts on this? Thanks all.
These are approximately 17 ft wide exterior stairs. They follow grade, so guards are not an issue. Required width is 140" based on occupant load.
Handrails are situated as follows, from one side to the other. 30" to the first handrail from the side, approximately 6 ft to the center handrail, then 6 ft to the next handrail, and 30" again to the opposite side. 3 handrails total.
No handrails on the "sides", as the person using the stairs on either side would have a handrail on one side of them, and the edge of the stairs on the other side of them.
They have 180" of width that is within 30" of a handrail.
Code states handrails are required on both sides of stairs. It would appear that they meet the intermediate handrail requirements of 1012.9, but not the requirement for handrails on both sides, per 1009.12.
Any thoughts on this? Thanks all.