• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

IP power supply

Just John

Bronze Member
Joined
Jan 29, 2010
Messages
65
2009 IFC 907.7.2 Power Supply. The primary and secondary power supply for the fire alarm system shall be provided in accordance with NFPA 72.

The Silent Knight IP fire alarm communicators are UL 864 listed for signaling under Other Transmission Technologies and comply with NFPA 72 requirements.

The installation requirements state - Although not required to meet NFPA, a small UPS is recommended to provide backup power for customer-provided router/switch

Question: Is it your opinion that the above IFC requires the UPS?
 