Glenn M. input might help with this.
I notice a new table with footnote C in 2012 & 2015 seems at odds with footnote f. The 2012 AWC Deck Detail is where I found the info for MPCWP.
2009 TABLE R502.2.2.1
f. When solid-sawn pressure-preservative-treated deck ledgers are attached to a minimum 1 inch thick engineered wood product (structural composite lumber, laminated veneer lumber or wood structural panel band joist), the ledger attachment shall be designed in accordance with accepted engineering practice.
2012 R507.2 Deck ledger connection to band joist.
For decks supporting a total design load of 50 pounds per square foot (2394 Pa) [40 pounds per square foot (1915 Pa) live load plus 10 pounds per square foot (479 Pa) dead load], the connection between a deck ledger of pressure-preservative-treated Southern Pine, incised pressure-preservative-treated Hem-Fir or
approved decay-resistant species, and a 2-inch (51 mm) nominal lumber band joist bearing on a sill plate or wall plate shall be constructed with
1/
2-inch (12.7 mm) lag screws or bolts with washers in accordance with Table R507.2. Lag screws, bolts and washers shall be hot-dipped galvanized or stainless steel.
TABLE R507.2 FASTENER SPACING FOR A SOUTHERN PINE OR HEM-FIR DECK LEDGER AND A 2-INCH-NOMINAL SOLID-SAWN SPRUCE-PINE-FIR BAND JOISTc, f, g (Deck live load = 40 psf, deck dead load = 10 psf)
|
|
1/2 inch diameter lag screw with 15/32 inch
maximum sheathinga
|
1/2 inch diameter bolt with 15/32 inch maximum sheathing
|
1/2 inch diameter bolt with 15/32 inch maximum sheathing and 1/2 inch stacked washersb, h
|
[TD=align: center]
JOIST SPAN
[/TD]
[TD=align: center]
6′ and less
[/TD]
[TD=align: center]
6′ 1″ to 8′
[/TD]
[TD=align: center]
8′ 1″ to 10′
[/TD]
[TD=align: center]
10′ 1″ to 12′
[/TD]
[TD=align: center]
12′ 1″ to 14′
[/TD]
[TD=align: center]
14′ 1″ to 16′
[/TD]
[TD=align: center]
16′ 1″ to 18′
[/TD]
[TD=align: center]
Connection details
[/TD]
[TD=colspan: 7, align: center]
On-center spacing of fasteners
d, e
[/TD]
[TD=align: center]30
[/TD]
[TD=align: center]23
[/TD]
[TD=align: center]18
[/TD]
[TD=align: center]15
[/TD]
[TD=align: center]13
[/TD]
[TD=align: center]11
[/TD]
[TD=align: center]10
[/TD]
[TD=align: center]36
[/TD]
[TD=align: center]36
[/TD]
[TD=align: center]34
[/TD]
[TD=align: center]29
[/TD]
[TD=align: center]24
[/TD]
[TD=align: center]21
[/TD]
[TD=align: center]19
[/TD]
[TD=align: center]36
[/TD]
[TD=align: center]36
[/TD]
[TD=align: center]29
[/TD]
[TD=align: center]24
[/TD]
[TD=align: center]21
[/TD]
[TD=align: center]18
[/TD]
[TD=align: center]16
[/TD]
For SI: 1 inch = 25.4 mm, 1 foot = 304.8 mm. 1 pound per square foot = 0.0479 kPa.
|
a. The tip of the lag screw shall fully extend beyond the inside face of the band joist.
|
b. The maximum gap between the face of the ledger board and face of the wall sheathing shall be 1/2 inch.
|
c. Ledgers shall be flashed to prevent water from contacting the house band joist.
|
d. Lag screws and bolts shall be staggered in accordance with :Next('./icod_irc_2012_5_par090.htm')'>Section R507.2.1.
|
e. Deck ledger shall be minimum 2 × 8 pressure-preservative-treated No. 2 grade lumber, or other approved materials as established by standard engineering practice.
|
f. When solid-sawn pressure-preservative-treated deck ledgers are attached to a minimum 1-inch-thick engineered wood product (structural composite lumber, laminated veneer lumber or wood structural panel band joist), the ledger attachment shall be designed in accordance with accepted engineering practice.
|
g. A minimum 1 × 91/2 Douglas Fir laminated veneer lumber rimboard shall be permitted in lieu of the 2-inch nominal band joist.
|
h. Wood structural panel sheathing, gypsum board sheathing or foam sheathing not exceeding 1 inch in thickness shall be permitted. The maximum distance between the face of the ledger board and the face of the band joist shall be 1 inch.
|
R507.2.1 Placement of lag screws or bolts in deck ledgers and band joists.
The lag screws or bolts in deck ledgers and band joists shall be placed in accordance with Table R507.2.1 and Figures R507.2.1(1) and R507.2.1(2).
TABLE 507.2.1 PLACEMENT OF LAG SCREWS AND BOLTS IN DECK LEDGERS AND BAND JOISTS
[TD=colspan: 5, align: center]
MINIMUM END AND EDGE DISTANCES AND SPACING BETWEEN ROWS
[/TD]
[TD=align: center][/TD]
[TD=align: center]
TOP EDGE
[/TD]
[TD=align: center]
BOTTOM EDGE
[/TD]
[TD=align: center]
ENDS
[/TD]
[TD=align: center]
ROW SPACING
[/TD]
[TD=align: center]2 inches
d
[/TD]
[TD=align: center]
1
/
4
inch
[/TD]
[TD=align: center]2 inches
b
[/TD]
[TD=align: center]1
5
/
8
inches
b
[/TD]
[TD=align: center]
3
/
4
inch
[/TD]
[TD=align: center]2 inches
[/TD]
[TD=align: center]2 inches
b
[/TD]
[TD=align: center]1
5
/
8
inches
b
[/TD]
For SI: 1 inch = 25.4 mm.
|
a. Lag screws or bolts shall be staggered from the top to the bottom along the horizontal run of the deck ledger in accordance with Figure R507.2.1(1).
|
b. Maximum 5 inches.
|
c. For engineered rim joists, the manufacturer’s recommendations shall govern.
|
d. The minimum distance from bottom row of lag screws or bolts to the top edge of the ledger shall be in accordance with Figure R507.2.1(1).
|