• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Is a damper needed here?

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
3,075
Location
Southern California
Type V-A apartment building. Ceiling membrane at top floor is part of 1 hour roof assembly.
Ducts are rigid spiral. Attic provides space to route ducts from HVAC closet to ceiling registers.
Have you seen any typical UL F-C penetration that addresses this issue?



1706557670689.png
 
Definitely needs a ceiling radiation damper with this setup, both at the mechanical closet lid and at the register locations. The other option would be to maintain the dwelling unit separation up through the attic to the bottom side of the roof deck if that's even possible based on trusses/rafters.
 
Definitely needs a ceiling radiation damper with this setup, both at the mechanical closet lid and at the register locations. The other option would be to maintain the dwelling unit separation up through the attic to the bottom side of the roof deck if that's even possible based on trusses/rafters.
If I maintain the unit separation, do I still need a ceiling damper? (due to Type V-1hr construction, achieved via ceiling membrane on the roof trusses).
 
The problem is that if your separation is the ceiling membrane, each duct penetration is an opening in it that needs to be protected. In the IMC, there are no exceptions for duct penetrations of rated horizontal assemblies.
 
Based upon the size of the duct you wouldn't meet any exception/s in 716.5.2 and would need dampers in place at each penetration
 