1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Is a Fire Pump Room a Wet Location?

Discussion in 'Electrical Codes' started by jar546, Dec 20, 2018.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,648
    Likes Received:
    707
    Do any of you, in your right mind, consider a fire-pump room to be a wet location because it has a lot of water pipes?

    Do you? What would be the reasoning if you do?
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,965
    Likes Received:
    1,244
    cannot speak to electrical question,

    But normally there is water on the floor from something associated with the pump set up
     
  3. Msradell

    Msradell Sawhorse

    Joined:
    Jul 23, 2011
    Messages:
    878
    Likes Received:
    93
    No it's not a wet location anymore than the area in the residential basement where you have hot water heaters etc. is a wet area. Just because there are a lot of pipes giving moderate doesn't make it a wet area.
     
  4. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    7,118
    Likes Received:
    1,056
    Absolutely not unless there is some sort of required maintenance/ flushing that soaks the room, but I have not seen THAT fire pump yet....
     
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,965
    Likes Received:
    1,244
    Is there a definition for

    Wet location
     
  6. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,271
    Likes Received:
    473
    I would not consider a Fire Pump Room a wet location, hopefully there's a floor drain if used for other appliances like a WH.
     
  7. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,865
    Likes Received:
    283
    & = & = &
    Electrically speaking, ...Yes !..........From the NEC:
    Location, Wet: "Installations underground or in concrete slabs or masonry in
    direct contact with the earth; in locations subject to saturation with water or
    other liquids, such as vehicle washing areas; and in unprotected locations
    exposed to weather".

    & = & = &
     
    cda likes this.
  8. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,648
    Likes Received:
    707
    The only time a fire-pump room gets wet is if there is a failure of a component. I do not agree to call it a wet location. If that is the case then every room in a house or building that has plumbing is a wet location.
     
  9. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,965
    Likes Received:
    1,244
    Ok per the definition not a wet location

    Just some of them not a nice place to be with the pump running, and you are the one who has to trust the electrical install

    When you decide to touch the controller and there is some water on the ground
     
  10. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,346
    Likes Received:
    368
    IT depends --- Had one fire pump that dumped cooling water onto the slab trench drain to filter and return to lake ----- So in short the splashing of the water into a badly designed trench drain system made almost everything wet about 30 minutes into the fire pump acceptance test.
     
    jar546 likes this.
  11. Gregg Harris

    Gregg Harris Saw Horse

    Joined:
    Jan 17, 2012
    Messages:
    909
    Likes Received:
    14

    Not a wet location by definition
     
  12. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,648
    Likes Received:
    707
    OK let's open this back up. Chris K brought this to my attention in NEC 695.12(E)

    (E) Protection Against Pump Water. Fire pump controller and
    power transfer switches shall be located or protected so that
    they are not damaged by water escaping from pumps or pump
    connections.

    So what does this mean to you? A change in NEMA rating for the transfer switches and fire pump controller or simply placing a barrier around them to protect them? There are a lot of pump connections in a pump room...
    Thoughts?
     
  13. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    7,118
    Likes Received:
    1,056
    I ASSUME that means water escaping from normal operation such as BB mentioned, not failure because....Well it's already failing....
     
  14. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,965
    Likes Received:
    1,244

    locate fire pump and controller off the ground



    http://1-888-builder.com/wp-content/gallery/portraits/1-41.jpg
     
  15. TorrinFu

    TorrinFu Registered User

    Joined:
    May 8, 2020
    Messages:
    1
    Likes Received:
    0
    Hi...i was going through a reading material and found that It is not a wet location as defined in the NEC. But this is sure that some requirements along these lines. The listing standards for fire pump controllers requires the controller to be drip proof and the NEC and NFPA 20 has some requirements to not violate the integrity of the controller enclosure.
     