Read the police blotter this morning, yes it's a small town and is published daily, a couple was "trapped" in the carwash when the overhead doors failed to open after the carwash was complete. for those of you in the southern climates our un-attended automatic carwashes have garage doors on each end that open after you pay, you drive in the door closes the car is washed and the other door opens and you drive out , There was a mal***tion that prevented the door from opening and they could not get out. They could not manually open the overhead door either.
Should there be an exit door from such a facility? I don't believe any of the exceptions would apply if the facility was built today.
Opinions?
1008.1.2 Door swing.
Egress doors shall be of the pivoted or side-hinged swinging type.
Exceptions:
1. Private garages, office areas, factory and storage areas with an occupant load of 10 or less.
2. Group I-3 occupancies used as a place of detention.
3. Critical or intensive care patient rooms within suites of health care facilities.
4. Doors within or serving a single dwelling unit in Groups R-2 and R-3.
5. In other than Group H occupancies, revolving doors complying with Section 1008.1.4.1.
6. In other than Group H occupancies, horizontal sliding doors complying with Section 1008.1.4.3 are permitted in a means of egress .
7. Power-operated doors in accordance with Section 1008.1.4.2.
8. Doors serving a bathroom within an individual sleeping unit in Group R-1.
9. In other than Group H occupancies, manually operated horizontal sliding doors are permitted in a means of egress from spaces with an occupant load of 10 or less.
Doors shall swing in the direction of egress travel where serving an occupant load of 50 or more persons or a Group H occupancy.
Should there be an exit door from such a facility? I don't believe any of the exceptions would apply if the facility was built today.
Opinions?
1008.1.2 Door swing.
Egress doors shall be of the pivoted or side-hinged swinging type.
Exceptions:
1. Private garages, office areas, factory and storage areas with an occupant load of 10 or less.
2. Group I-3 occupancies used as a place of detention.
3. Critical or intensive care patient rooms within suites of health care facilities.
4. Doors within or serving a single dwelling unit in Groups R-2 and R-3.
5. In other than Group H occupancies, revolving doors complying with Section 1008.1.4.1.
6. In other than Group H occupancies, horizontal sliding doors complying with Section 1008.1.4.3 are permitted in a means of egress .
7. Power-operated doors in accordance with Section 1008.1.4.2.
8. Doors serving a bathroom within an individual sleeping unit in Group R-1.
9. In other than Group H occupancies, manually operated horizontal sliding doors are permitted in a means of egress from spaces with an occupant load of 10 or less.
Doors shall swing in the direction of egress travel where serving an occupant load of 50 or more persons or a Group H occupancy.