Oh Well
There is a mechanical permit to install an appliance. (wall furnace) Therefor an approved shutoff valve is required. Well we haven't reached a point where the old valve shall be replaced because it was approved 60 years ago.1313.4 Appliance Shutoff Valves and Connections. Appliances connected to a piping system shall have an accessible, approved manual shutoff valve.......
There is this section that lends itself to abuse:
But take a look at the requirements for a valve beyond an AHJ approval.107.3.2 The Authority Having Jurisdiction shall have the authority to require tests to be made or repeated if, at any time,
there is reason to believe that any material or device no longer conforms to the requirements on which its approval was based.
Shutoff valves of size 1 inch National Pipe Thread and smaller shall be listed1309.10 Shutoff Valves. Shutoff valves shall be approved and shall be selected giving consideration to pressure drop, service involved, emergency use,
and reliability of operation. Shutoff valves of size 1 inch National Pipe Thread and smaller shall be listed. [NFPA 54:5.12]
It could be that the old valve had a listing 60 years ago.
Or perhaps the concept of "listed" wasn't born yet.
The old valves listing status is not important.
The listing for the valve that will serve the new appliance is the listing that's required.
That Listing won't be 60 years old.
Why do you suppose a valve larger than 1" NPT isn't required to be listed?
One thing that I didn't find is the requirement that a shutoff valve not require the use of a tool. Appendix? Anybody know where that is now?
Backing up to the OP. I didn't ask if the use of a 60 year old valve was a code violation. I asked if it was ethical. Ethical was lost to code violation. I also didn't stipulate how I apply the pencil regarding old valves.
I don't know why there was so much confusion...it's right there in the code.