Is This a Dead End?

Phil B

SAWHORSE
Joined
Sep 15, 2018
Messages
227
Location
Florida
The green lines indicate the path to the exit in the sketch below. Is a dead end condition created if the room at the end of the corridor has an opening at point 'A" without a door thus allowing someone to conceivably enter the room in an emergency exit situation?

Is it a Dead End.jpg
 
If the door at the end of the corridor (the location of your second arrow) is always unlocked and available for egress, then you do not have a dead-end corridor. However, there should be an EXIT sign over that door, and another EXIT sign with the right directional chevron illuminated above the door to the room. Depending on the type of facility and the use of that room, you might also request that that door be marked "NOT AN EXIT."
 
As long as you have appropriate exit signage, that shouldn't be a dead end corridor. That said, I agree with JPohling. That layout probably isn't the best. I typically don't like to put doors at the end of corridors (where the opening could be easily confused as an exit or is otherwise visible from the opposite end of the corridor) like what your showing unless it's an exit or exit access doorway.
 
As long as you have appropriate exit signage, that shouldn't be a dead end corridor. That said, I agree with JPohling. That layout probably isn't the best. I typically don't like to put doors at the end of corridors (where the opening could be easily confused as an exit or is otherwise visible from the opposite end of the corridor) like what your showing unless it's an exit or exit access doorway.
Thank you both!!
 
If the door at the end of the corridor (the location of your second arrow) is always unlocked and available for egress, then you do not have a dead-end corridor. However, there should be an EXIT sign over that door, and another EXIT sign with the right directional chevron illuminated above the door to the room. Depending on the type of facility and the use of that room, you might also request that that door be marked "NOT AN EXIT."
There is no door leading into the room, it is a cased opening. In an emergency someone could proceed directly into the room. An exit sign and arrow to the exit door located on the hallway side would be prudent.
 
There is no door leading into the room, it is a cased opening. In an emergency someone could proceed directly into the room. An exit sign and arrow to the exit door located on the hallway side would be prudent.

Ops -- I missed the omission of a door at the entrance to the room. Irrespective, a directional EXIT sign is not just a good idea at the corner of the corridor, it's required because you can't see the exit door from the upper part of the corridor.

1013.1 Where required. Exits and exit access doors shall be
marked by an approved exit sign readily visible from any
direction of egress travel. The path of egress travel to exits and
within exits shall be marked by readily visible exit signs to
clearly indicate the direction of egress travel in cases where the
exit or the path of egress travel is not immediately visible to

the occupants. Intervening means of egress doors within exits
shall be marked by exit signs. Exit sign placement shall be
such that any point in an exit access corridor or exit passageway
is within 100 feet (30 480 mm) or the listed viewing
distance of the sign, whichever is less, from the nearest visible
exit sign.
 
There is no door leading into the room, it is a cased opening. In an emergency someone could proceed directly into the room. An exit sign and arrow to the exit door located on the hallway side would be prudent.
Here is the overall exit configuration if that helps. The yellow highlighted are is the one where the cased opening will be. directional exit signs will be sued as required. The areas with an 'L' are mostly low walls with no internal rooms. I agree woot the thinking that wandering thru the cased opening may be a concern.

Is it a Dead End - 2.jpg
 
It's still not a dead-end corridor, but it still needs a directional EXIT sign above the cased opening at the corner of the corridor. From the 2021 IBC:

1013.1 Where required. Exits and exit access doors shall be
marked by an approved exit sign readily visible from any
direction of egress travel.
The path of egress travel to exits and
within exits shall be marked by readily visible exit signs to
clearly indicate the direction of egress travel in cases where the
exit or the path of egress travel is not immediately visible to
the occupants
. Intervening means of egress doors within exits
shall be marked by exit signs. Exit sign placement shall be
such that any point in an exit access corridor or exit passageway
is within 100 feet (30 480 mm) or the listed viewing
distance of the sign, whichever is less, from the nearest visible
exit sign.
 