Thanks for the replies.
Corridors are still not clear to me.
As Builder Bob stated, the definition of corridor is "An enclosed exit access component that defines
and provides a path of egress travel to an exit." Can someone define it using different words for me?
What is the definition of enclosed in this context? Full height walls, a ceiling, and a floor? Full height walls, a ceiling, a floor, and doors at both ends?
This "area" on the sketch has a floor, a ceiling, and walls to the ceiling. It provides a path of egress travel from the seating area to the second required exit - the double doors leading to the exterior deck. If occupants need to travel through this box, why would it not be considered a corridor?
Is this not a corridor because there are no occupiable spaces on either side?
When would this area be considered a corridor?
If doors were added to separate the seating area from this area, would it now be considered a corridor?:banghd
Maybe I need some of these . . . :chpill :chpill :chpill.
To answer some of Builder Bob's questions/concerns.
My area of concern are the following:Undetermined deck size and occupant load which should have an impact of the number which of
plumbing fixtures required.
Inside occupant load is 99. Any more and the building needs sprinklers. The AHJ is working with us as this is a landmark building from way back when. I found an article stating the building existed in 1840, but I can not determine when it was built. Sufficient plumbing fixtures will be provided for the indoor and outdoor occupants.
storage under the stairs...
These are new stairs leading to an existing area below the first floor, which is just utility space. This area could be a crawl space with less than 7 ft clearance or a basement with projections every foot in the form of floor joists. So I guess dirt will be stored under the stairs. The :chpill is kicking in. :lol:
accessibility for the deck area
Accessibility is through the building. Egress will be another issue, probably discussed in a separate thread.
stairway width, handrails, guards,
All items will be designed to meet code.