Joint Compound Inside Electrical Box

jar546

CBO
Joined
Oct 16, 2009
Messages
13,000
Location
Not where I really want to be
It is normal to see some joint compound inside electrical boxed BEFORE they are trimmed out but afterwards can create an entirely new issue. In this case, there was work done after the electrician did the trim out.

What code section would you cite for this violation?

37A3BA92-B487-434E-82E6-446512A1C28F.JPG
 
The "ICE" code "It isn't correct so fix it"


I can't imagine anyone asking for a code section....but if it were to happen I would start with this:

110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
 
I can't imagine anyone asking for a code section....but if it were to happen I would start with this:

110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.

I'm not sure I agree with that one
 
I have some ideas:

406.5(G) Receptacles shall be enclosed so that live wiring terminals are not exposed to contact

110.7 Wiring Integrity. Completed wiring installations shall be free from short circuits, ground faults, or any connections to ground other than as required or permitted elsewhere in this code.

110.11 Deteriorating agents. I would use "other agents"

But here is the biggie and the one that applies:


110.12(B) Integrity of Electrical Equipment and Connections.
Internal parts of electrical equipment, including busbars, wiring
terminals, insulators, and other surfaces, shall not be damaged
or contaminated by foreign materials such as paint, plaster,
cleaners, abrasives, or corrosive residues. There shall be no
damaged parts that may adversely affect safe operation or
mechanical strength of the equipment such as parts that are
broken; bent; cut; or deteriorated by corrosion, chemical
action, or overheating.
 
Apppendix Q IRC Crosses NEC to IRC Sections
E3404.7 Integrity of electrical equipment 110.12(B)

2012 IRC
E3404.7 Integrity of electrical equipment.
Internal parts of electrical equipment, including busbars, wiring terminals, insulators and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners or abrasives, and corrosive residues. There shall not be any damaged parts that might adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; deteriorated by corrosion, chemical action, or overheating. Foreign debris shall be removed from equipment.
 