• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Joist hanger size

e hilton

Bronze Member
Joined
Jul 2, 2014
Messages
3,132
Location
Virginia
IBC 2015. Where can i find the requirements for joist hanger sizes? For example ... for a 2x10 joist, are you required to use a 2x10 hanger?
 
You will a different hangar number and hangar height as you graduate from 2x4 to 2x6 to 2x8, etc. etc. until you get to 2x10 and 2x12 where some of the hangars are the same size and some are larger but most are larger (taller). It essentially seems as though the wider the joists, the taller the hangars.
 
Load capacity is most of what matters, but there are some notes in there about lateral restraint vs. hanger height vs. joist height....
 
Deck screws? We always use sheetrock screws.

Seriously ... i was aware of the simpson design info, I was asking if there is a code section that applies. Or is this a case where code says to follow manufacturers requirements?
 
Many Simpson Strong-Tie connectors have been designed and tested for use with specific types and sizes of fasteners. The specified quantity, type and size of fastener must be installed in the correct holes on the connector to achieve published loads. Other factors such as fastener material and finish are also important. Incorrect fastener selection or installation can compromise connector performance and could lead to failure.
https://www.strongtie.com/products/...tors/technical-notes/fastener-types-and-sizes
 
R502.6 Bearing. The ends of each joist, beam or girder shall
have not less than 11/2 inches (38 mm) of bearing on wood or
metal and not less than 3 inches (76 mm) on masonry or concrete
except where supported on a 1-inch by 4-inch (25 mm
by 102 mm) ribbon strip and nailed to the adjacent stud or by
the use of approved joist hangers.

Whatever you want to approve....ICC ES or manufacturers engineering/ instructions.....Or nothing...
 
Simpson will tell you the depth needs to be 60% of the member assuming the correct fasteners and capacity is met...while under construction to prevent rotation. After another approved method is provided to prevent rotation this wouldn't apply. So if an lus24 will carry the load on a 2x10, it may work if bracing is provided. See note L in the link.

https://www.strongtie.com/products/...technical-notes/instructions-for-the-designer
 