Is anyone familiar with these "Kurt Keys" for ensuring disconnect between a portable generator and the MDP of a 4000A service?

Don't know if it is Kurt Key, or Curt Key or Kirt Key. Have no idea, no specs given.
 
This product may not be suitable for this application. Section 702.6 of the 2011 NEC requires the transfer equipment to be suitable for the intended use. Many jurisdictions determine suitability of a product based on listing. Transfer equipment is listed under UL 1008. Kirk Key systems do not meet the requirements of this standard. Even Kirk Key indicates their website what NEC sections apply. Artilce 700, 701, and 702 are NOT listed...

• NEC Article 440-33 Air-Conditioning and Refrigeration Equipment.• NEC Article 440-34 Air-Conditioning and Refrigeration Equipment.

• NEC Article 460-24 Switching.

• NEC Article 490-21 Circuit Interrupting Devices, High-Voltage Fuses.

• NEC Article 490-22 Equipment Over 600 Volts, Isolating Means.

• NEC Article 490-42 Interlocks - Interrupter Switches.

• NEC Article 490-45 Interlocks - Circuit Breakers.

• NEC Article 665-22 Guarding, Grounding, and Labeling.

• NEC Article 710-22 Isolating Means.

• NEC Article 710-24 Metal-Enclosed Power Switchgear and Industrial Control Assemblies.

• NEC Article 810-71 Interior Installation - Transmitting Stations.
 