2015 IBC
Proposed 3 story fully sprinkled non-separated F-1, S-2 occupancy addition to an existing 3 story B, F-1, S-2 occupancy. The existing building is partially sprinkled and partially separated by fire walls. The proposed and existing buildings will be separated via a 3 hr fire wall with one fire door on the first floor and one fire door on the second floor; both fire doors will be normally held open by fusible links.
The entire third floor of the proposed building is a refrigeration room, about 8,700 sf, with a 29 person occupant load. Per Table 1006.2.1, more than 1 exit or exit access doorway is required.
Section 1006.2.2.2 Refrigeration machinery rooms allows one exit access doorway to be served by a fixed ladder or alternating tread device.
Since the entire floor is a refrigeration machinery room, am I permitted to use a fixed ladder in one of the means of egress for the third floor?
Assuming a fixed ladder is allowed:
Is a fire rated shaft required? Section 1019 Exit Access Stairways and Ramps allows for openings without a shaft, but this is a ladder, not a stairway or a ramp. This ladder between the 2nd and 3rd floors is the only proposed unprotected opening to the 2nd floor.
Since the proposed first and second floors are connected to the existing building with normally held open fire doors, must I evaluate the existing building to see if the 2nd floor has unprotected openings to the 1st floor?
Section 1019.3 Occupancies other than Groups I-2 and I-3. In other than Group I-2 and I-3 occupancies, floor openings containing exit access stairways or ramps that do not comply with one of the conditions listed in this section shall be enclosed with a shaft enclosure constructed in accordance with Section 713.
1. Exit access stairways and ramps that serve or atmospherically communicate between only two stories. Such interconnected stories shall not be open to other stories. Again, the fire doors are held open with fusible links. If the existing building is open to more than two stories, would the proposed building be considered open to more than two stories since the fire doors are held open?
2 & 3 Omitted as these do not apply.
4. Exit access stairways and ramps in buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, where the area of the vertical opening between stories does not exceed twice the horizontal projected area of the stairway or ramp and the opening is protected by a draft curtain and closely spaced sprinklers in accordance with NFPA 13. In other than Group B and M occupancies, this provision is limited to openings that do not connect more than four stories. This might be applicable, if the dimension of the ladder cage can be considered part of the projected horizontal area.
5 - 8 Omitted as these do not apply.
In case anyone is wondering, the floor construction per Table 601 does not require a fire rating.
Proposed 3 story fully sprinkled non-separated F-1, S-2 occupancy addition to an existing 3 story B, F-1, S-2 occupancy. The existing building is partially sprinkled and partially separated by fire walls. The proposed and existing buildings will be separated via a 3 hr fire wall with one fire door on the first floor and one fire door on the second floor; both fire doors will be normally held open by fusible links.
The entire third floor of the proposed building is a refrigeration room, about 8,700 sf, with a 29 person occupant load. Per Table 1006.2.1, more than 1 exit or exit access doorway is required.
Section 1006.2.2.2 Refrigeration machinery rooms allows one exit access doorway to be served by a fixed ladder or alternating tread device.
Since the entire floor is a refrigeration machinery room, am I permitted to use a fixed ladder in one of the means of egress for the third floor?
Assuming a fixed ladder is allowed:
Is a fire rated shaft required? Section 1019 Exit Access Stairways and Ramps allows for openings without a shaft, but this is a ladder, not a stairway or a ramp. This ladder between the 2nd and 3rd floors is the only proposed unprotected opening to the 2nd floor.
Since the proposed first and second floors are connected to the existing building with normally held open fire doors, must I evaluate the existing building to see if the 2nd floor has unprotected openings to the 1st floor?
Section 1019.3 Occupancies other than Groups I-2 and I-3. In other than Group I-2 and I-3 occupancies, floor openings containing exit access stairways or ramps that do not comply with one of the conditions listed in this section shall be enclosed with a shaft enclosure constructed in accordance with Section 713.
1. Exit access stairways and ramps that serve or atmospherically communicate between only two stories. Such interconnected stories shall not be open to other stories. Again, the fire doors are held open with fusible links. If the existing building is open to more than two stories, would the proposed building be considered open to more than two stories since the fire doors are held open?
2 & 3 Omitted as these do not apply.
4. Exit access stairways and ramps in buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, where the area of the vertical opening between stories does not exceed twice the horizontal projected area of the stairway or ramp and the opening is protected by a draft curtain and closely spaced sprinklers in accordance with NFPA 13. In other than Group B and M occupancies, this provision is limited to openings that do not connect more than four stories. This might be applicable, if the dimension of the ladder cage can be considered part of the projected horizontal area.
5 - 8 Omitted as these do not apply.
In case anyone is wondering, the floor construction per Table 601 does not require a fire rating.
The sprinkler is required for increased floor area, increased number of stories, Group F-1 Fire area greater than 12,000 sf, combined F-1 Fire area on all floors exceeds 24,000 sf, and insufficient exterior wall openings.
Thanks if you made it to the end and have any thoughts.