jar546
CBO
Fire sprinklers are required under certain conditions for a Level 3 renovation and that points to Chapter 8 of the Existing Building Code (your IEBC, my FBC Existing. The language is almost identical, however and reads this way in Chapter 8:
804.2.2Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2.
In buildings with occupancies in Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2, work areas that have exits or corridors shared by more than one tenant or that have exits or corridors serving an occupant load greater than 30 shall be provided with automatic sprinkler protection where all of the following conditions occur:
So when we look at the example below, you will see that there is an open entryway to the 3 units. At the top of the exterior stairs you can go left into D1 for unit 1, go straight through D2 to get to the 2nd floor unit 2 or make a right and go through D3 which leads to unit 3. Out the back, the 2 lower units exit to grade through sliders and the 2nd floor unit uses the stairs you see and an exterior spiral staircase. Therefore, they do not share any corridors and each has their own exits. With that being said, I don't see how they can be mandated to install fire sprinklers.
To give you some context, this was a 4 unit NS with 2 up and 2 down undergoing a major renovation which includes turning the 2 units upstairs into one large one, renovations to the lower units and changing the layout of the structure. Here is the front entrance as described: Thoughts? FS or no FS?

804.2.2Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2.
In buildings with occupancies in Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2, work areas that have exits or corridors shared by more than one tenant or that have exits or corridors serving an occupant load greater than 30 shall be provided with automatic sprinkler protection where all of the following conditions occur:
- 1.The work area is required to be provided with automatic sprinkler protection in accordance with the Florida Building Code, Building as applicable to new construction; and
- 2.The work area exceeds 50 percent of the floor area.
So when we look at the example below, you will see that there is an open entryway to the 3 units. At the top of the exterior stairs you can go left into D1 for unit 1, go straight through D2 to get to the 2nd floor unit 2 or make a right and go through D3 which leads to unit 3. Out the back, the 2 lower units exit to grade through sliders and the 2nd floor unit uses the stairs you see and an exterior spiral staircase. Therefore, they do not share any corridors and each has their own exits. With that being said, I don't see how they can be mandated to install fire sprinklers.
To give you some context, this was a 4 unit NS with 2 up and 2 down undergoing a major renovation which includes turning the 2 units upstairs into one large one, renovations to the lower units and changing the layout of the structure. Here is the front entrance as described: Thoughts? FS or no FS?