First, hello everybody. I have been reading here for a while and find this sort of Forum very interesting and helpful.
We have designed a Hotel here in Miami and have recently received comments from the Fire Department.
The building is a 6 story structure - fully sprinklered.
One of the comments is regarding Elevator Lobby doors to enclose the Elevator lobbies on every floor.
As per the Florida Building Code this is not required as per 708.14.1 Exception #4
NFPA does not require it either unless the Elevators are being proposed as an additional means of egress (which they are not)
I pointed this out to the reviewer and he says he is requesting the doors to avoid the smoke going up through the elevator shaft and going out through the hoistway doors and entering the corridors.
Isn't the purpose of the Elevator Lobby doors to keep the smoke from entering the lobby and NOT from escaping to the corridor?
The other comment has to do with NFPA 1
The comment is "Comply with 'In building public safety radio enhancement system'" and he goes on to ask for a 10' x 10' room on the roof with AC and Emergency lighting.
He later cited NFPA 1-11.10 which says nothing about a room and only talks about maintaining a certain level of signal strength.
I think the 10' x 10 room requirement is a little over the top. Has anyone heard of this or had to comply with something like this before in such a small building?
Is there a common solution to resolve the enhancement of radio signals inside a building?
I hope I have been clear enough in my explanation.
I thank you all in advance for your help.
Gonzalo
We have designed a Hotel here in Miami and have recently received comments from the Fire Department.
The building is a 6 story structure - fully sprinklered.
One of the comments is regarding Elevator Lobby doors to enclose the Elevator lobbies on every floor.
As per the Florida Building Code this is not required as per 708.14.1 Exception #4
NFPA does not require it either unless the Elevators are being proposed as an additional means of egress (which they are not)
I pointed this out to the reviewer and he says he is requesting the doors to avoid the smoke going up through the elevator shaft and going out through the hoistway doors and entering the corridors.
Isn't the purpose of the Elevator Lobby doors to keep the smoke from entering the lobby and NOT from escaping to the corridor?
The other comment has to do with NFPA 1
The comment is "Comply with 'In building public safety radio enhancement system'" and he goes on to ask for a 10' x 10' room on the roof with AC and Emergency lighting.
He later cited NFPA 1-11.10 which says nothing about a room and only talks about maintaining a certain level of signal strength.
I think the 10' x 10 room requirement is a little over the top. Has anyone heard of this or had to comply with something like this before in such a small building?
Is there a common solution to resolve the enhancement of radio signals inside a building?
I hope I have been clear enough in my explanation.
I thank you all in advance for your help.
Gonzalo