Do the plans show the oven?? Do they show the location of the oven??Sifu said:This morning I requested the specifications on the hood with the caution that in all likelihood we would want a type II hood over them so we'll see what happens.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Do the plans show the oven?? Do they show the location of the oven??Sifu said:This morning I requested the specifications on the hood with the caution that in all likelihood we would want a type II hood over them so we'll see what happens.
Are there any other cooking appliances in the space???Sifu said:yes, says "oven" with a number reference for the schedule which says "owner supplied".
Ul 720 b wrong ul???zigmark said:For the sake of educational purposes I strongly suggest you contact UL regarding the light duty exception per the test requirements of UL 720B. Surprisingly, when recently researching this issue I was fortunate enough to get the author of this portion of UL 720B on the line. After hearing his description of how the test was performed I had a change of opinion about that allowance/requirement. Here is the short version of the test procedure;Set appliance at its' highest possible temperature setting. Insert "chicken". Wait the test determined amount of time (2-hours I believe). If the testing capture system does not detect the prescribed amount of smoke or grease then a Type II hood is sufficient. Otherwise a Type I hood is required.
Talking with UL the general impression was that most electric ovens that are capable of cooking food products over 250 degrees (I believe that was the temp. it was relatively low but I'm not in my office) fail this test. UL's description of appliances that passed the test were the countertop type warming devices and that this standard was implemented to address that specifically.
Regardless of what "we have always seen or required" the industry is moving toward requiring Type I hoods over more types of appliances, right , wrong or indifferent. The push for this according to UL was from the industry/manufacturers and not the regulation side which I found interesting.
I would strongly encourage you to contact UL and ask about that standard and test procedure, it is educational if nothing else.
ZIG
And therein is the problem. A design professional not following through with the owner to determine what is needed or will be used for a project. Happens all the time.The only reference I have found is to the oven with a schedule of appliances which indicates an owner supplied oven.
Zig, I'm sorry, I'm confused. What code section is your post referring (UL 710B) to; 507.1, Exception 2 or 507.2.1, Exception?zigmark said:For the sake of educational purposes I strongly suggest you contact UL regarding the light duty exception per the test requirements of UL 720B. Surprisingly, when recently researching this issue I was fortunate enough to get the author of this portion of UL 720B on the line. After hearing his description of how the test was performed I had a change of opinion about that allowance/requirement. Here is the short version of the test procedure;Set appliance at its' highest possible temperature setting. Insert "chicken". Wait the test determined amount of time (2-hours I believe). If the testing capture system does not detect the prescribed amount of smoke or grease then a Type II hood is sufficient. Otherwise a Type I hood is required.
Talking with UL the general impression was that most electric ovens that are capable of cooking food products over 250 degrees (I believe that was the temp. it was relatively low but I'm not in my office) fail this test. UL's description of appliances that passed the test were the countertop type warming devices and that this standard was implemented to address that specifically.
Regardless of what "we have always seen or required" the industry is moving toward requiring Type I hoods over more types of appliances, right , wrong or indifferent. The push for this according to UL was from the industry/manufacturers and not the regulation side which I found interesting.
I would strongly encourage you to contact UL and ask about that standard and test procedure, it is educational if nothing else.
ZIG
507.2.1 Type I hoods.rgrace said:Zig, I'm sorry, I'm confused. What code section is your post referring (UL 710B) to; 507.1, Exception 2 or 507.2.1, Exception?
Are there any other cooking appliances in the space???rgrace said:Zig, I'm sorry, I'm confused. What code section is your post referring (UL 710B) to; 507.1, Exception 2 or 507.2.1, Exception?