Some follow up on this. We met with the AHJ and reached the following conclusions:
This could be treated as a two-story atrium, no smoke control required. The separate shaft would be considered connecting more than two floors and need two hour fire barriers bounding it.
Attached is a more developed drawing of my first sketch showing these options.
So I could put a 2 hr glazed "floor" separating the atrium and shaft and then I would only need 1 hr barriers around the shaft.
Or... no horizontal separation between atrium and shaft and provide 2 hr barriers around the shaft (roughly $500,000 if you're curious, there are two of these shafts).
The "shutters" (in lieu of rated glazing) were less well received. 716 certainly allows shutters as an opening protective but I guess the question is - when does the "opening" become large enough that it's all opening and no barrier?
I want to at least consider using unrated storefront around the shaft with something like a Won-Door Moveable Fire Wall that they claim meets ASTM E-199.
What do you think about Won-Door as 2 hr barrier around the shaft? This would be where storefront is shown on attached (you're seeing one side out of 4, all the same size).
Thanks!
This could be treated as a two-story atrium, no smoke control required. The separate shaft would be considered connecting more than two floors and need two hour fire barriers bounding it.
Attached is a more developed drawing of my first sketch showing these options.
So I could put a 2 hr glazed "floor" separating the atrium and shaft and then I would only need 1 hr barriers around the shaft.
Or... no horizontal separation between atrium and shaft and provide 2 hr barriers around the shaft (roughly $500,000 if you're curious, there are two of these shafts).
The "shutters" (in lieu of rated glazing) were less well received. 716 certainly allows shutters as an opening protective but I guess the question is - when does the "opening" become large enough that it's all opening and no barrier?
I want to at least consider using unrated storefront around the shaft with something like a Won-Door Moveable Fire Wall that they claim meets ASTM E-199.
What do you think about Won-Door as 2 hr barrier around the shaft? This would be where storefront is shown on attached (you're seeing one side out of 4, all the same size).
Thanks!