I am not familiar with a code provision to support what I’m about to say, IBC 1010.1 addresses doors required as part of the means of egress but you’re saying the door you want to lock is not required.Can I permanently lock 2nd exit door (located in new office) to exterior when occupancy (occupant load 8) only requires single exit? "Not an exit sign" required?
You’re welcome. A keyed deadbolt would let you put the door back in service relatively easily in the future if you wanted.Thanks for the suggestion walker.t , I was thinking of a keyed deadbolt might work.
Good point, I erroneously focused only on occupant load without considering other requirements that could trigger the need a second exit.In addition to occupant load, you also need to address exit access travel distance and common path of travel distance.
1013.1 Where RequiredIn addition to occupant load, you also need to address exit access travel distance and common path of travel distance. If all those are okay, then you can permanently lock the second door. If it were in my jurisdiction, I would require a "NOT AN EXIT" sign, and I'm certain my fire marshal would agree. If there is an exit sign over that door, it will have to be removed.
You are asking if you can label an exit access stairway as an exit.see the exception that says the exit sign is not "required" if only one exit is required, but is it prohibited?
Because the exit access stairway is not a component of the exit system it should not be labeled as an exit.2018 IBC definition of “Exit Access Stairway”
A stairway within the exit access portion of the means of egress system.
Depending on the parameters of your building (such as size, whether it is sprinklered, and the location of other exits) you may not meet the exit access travel distance limitations (see IBC Table 1017.2) if you measure the path of travel down the exit access stairway. With that in mind, it may have been necessary to construct the exit stairway so people can reach a protected exit component within the exit access travel distance limitation.2018 IBC partial definition of “Exit”
That portion of a means of egress system between the exit access and exit discharge or public way. Exit components include…interior exit stairways…
I think the code is saying it’s safer to go down the stairway with the 2-hour rating. You know it’s going to be connected to a protected path that leads to the exit discharge, that exit access stairway may open to a lobby or some other area where there’s a fire.is it not safer to point occupants to that exit also?
2018 IBC 1022.1 (partial quote)
Once a given level of exit protection is achieved, such level of protection shall not be reduced until arrival at the exit discharge. Exits shall be continuous from the point of entry into the exit to the exit discharge.
You’re welcome!Thanks for the responses!
Each doorway or passage along an exit access that could be mistaken for an exit must be marked "Not an Exit" or similar designation, or be identified by a sign indicating its actual use ... OSHA
we do not enforce OSHA
I'm going to say nay, nay to that as we put exit signs in corridors and general circulation paths (exit access) all the time....You put braille signs at the "entrance to an exit" (IBC 1013.4), you put exit signs along the path to an exit....You are asking if you can label an exit access stairway as an exit.
Because the exit access stairway is not a component of the exit system it should not be labeled as an exit.
Depending on the parameters of your building (such as size, whether it is sprinklered, and the location of other exits) you may not meet the exit access travel distance limitations (see IBC Table 1017.2) if you measure the path of travel down the exit access stairway. With that in mind, it may have been necessary to construct the exit stairway so people can reach a protected exit component within the exit access travel distance limitation.
A scenario I can imagine is that a fire breaks out in the building, the exit access stairway (which doesn’t have a rating) catches on fire, occupants follow the exit sign to the exit access stairway and when they open the door the stairway is filled with smoke from the fire on the first floor. Then they need to turn around and follow the exit signs to the “real” exit stairway with the rating. With no exit sign on the door to the exit access stairway they head in the right direction the first time.
I think the code is saying it’s safer to go down the stairway with the 2-hour rating. You know it’s going to be connected to a protected path that leads to the exit discharge, that exit access stairway may open to a lobby or some other area where there’s a fire.
I don't agree. Exit signs are required (and should be permitted) at exit access components all the time. Lots of buildings where there is nothing but the exit discharge and plenty of exit signs required before you get there.You are asking if you can label an exit access stairway as an exit.
Because the exit access stairway is not a component of the exit system it should not be labeled as an exit.
Depending on the parameters of your building (such as size, whether it is sprinklered, and the location of other exits) you may not meet the exit access travel distance limitations (see IBC Table 1017.2) if you measure the path of travel down the exit access stairway. With that in mind, it may have been necessary to construct the exit stairway so people can reach a protected exit component within the exit access travel distance limitation.
A scenario I can imagine is that a fire breaks out in the building, the exit access stairway (which doesn’t have a rating) catches on fire, occupants follow the exit sign to the exit access stairway and when they open the door the stairway is filled with smoke from the fire on the first floor. Then they need to turn around and follow the exit signs to the “real” exit stairway with the rating. With no exit sign on the door to the exit access stairway they head in the right direction the first time.
I think the code is saying it’s safer to go down the stairway with the 2-hour rating. You know it’s going to be connected to a protected path that leads to the exit discharge, that exit access stairway may open to a lobby or some other area where there’s a fire.
I think we’re in agreement. You put exit signs along the path to an exit - I said that I thought the sign should be removed because it was leading to an exit access component.you put exit signs along the path to an exit....
That’s not the scenario described in #10. Seemed to me that if there are two stairs, one an exit access stairway and the other an exit stairway, that only the exit stairway should be labeled as an exit because that’s the protected path of egress travel.Lots of buildings where there is nothing but the exit discharge and plenty of exit signs required before you get there.
I don't believe it's labeling it as a code compliant "exit", as if John W Public would know the difference anyways, but is just directional signage leading to a way out of the building. And in this example both paths do lead to an exit eventually.I think we’re in agreement. You put exit signs along the path to an exit - I said that I thought the sign should be removed because it was leading to an exit access component.
That’s not the scenario described in #10. Seemed to me that if there are two stairs, one an exit access stairway and the other an exit stairway, that only the exit stairway should be labeled as an exit because that’s the protected path of egress travel.
Can I permanently lock 2nd exit door (located in new office) to exterior when occupancy (occupant load 8) only requires single exit? "Not an exit sign" required?
Your comment made me think of how we can’t conceal exit doors:Yes, a "NOT AN EXIT" sign would be required, and there should NOT be any "EXIT" signs directing occupants to the not-an-exit.
We have to make the egress system readily apparent - can’t hide an exit door or present a not-an-exit door in a manner to make it look like an exit door.Partial quote of 2018 IBC 1010.1
Means of egress doors shall not be concealed by curtains, drapes, decorations or similar materials.
What section that requires this.Yes, a "NOT AN EXIT" sign would be required
7.10.8.3.1
Any door, passage, or stairway that is neither an exit nor a way of exit access and that is located or arranged so that it is likely to be mistaken for an exit shall be identified by a sign that reads as follows:
NO
EXIT