For a full fire alarm system, where you have sleeping areas.
Low Frequency sounders are required in the sleeping areas.
NFPA 72:
18.4.5.3 *
Audible appliances provided for the sleeping areas to awaken occupants shall produce a low frequency alarm signal that complies with the following:
SO, recently have had a few fire alarm contractors interpret that to mean, besides each bedroom, the living room area also requires a low frequency sounder. I could almost agree with that, when I walk into some apartments and there is a full size bed in the living room.
Or, a so called Den/Office.
Anyone requiring low frequency anywhere besides actual labeled bedrooms???
Low Frequency sounders are required in the sleeping areas.
NFPA 72:
18.4.5.3 *
Audible appliances provided for the sleeping areas to awaken occupants shall produce a low frequency alarm signal that complies with the following:
- (1)
The alarm signal shall be a square wave or provide equivalent awakening ability.
- (2)
The waveform shall have a fundamental frequency of 520 Hz ± 10 percent.
- (3)*
The notification equipment shall be listed for producing the low frequency waveform.
SO, recently have had a few fire alarm contractors interpret that to mean, besides each bedroom, the living room area also requires a low frequency sounder. I could almost agree with that, when I walk into some apartments and there is a full size bed in the living room.
Or, a so called Den/Office.
Anyone requiring low frequency anywhere besides actual labeled bedrooms???