• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Massachusetts Plumbing Code

Codegeek

Registered User
Joined
Jun 17, 2011
Messages
717
Location
Kansas
I'm working on a retail store in MA and I'm having a heck of a time with their state plumbing code on figuring fixture counts. Is anyone familiar with the MA state plumbing code?

I have an occupant load of 2,804. According to what I'm finding it's 1 water closet per 20 people. There's no way they need that many water closets. Can someone help me?

Thanks!
 
A project we did a few years ago for a major retailer, we used 1:20 for employee restrooms and 1:750 for customers restrooms

Talk w/ your BO
 
I have a call into the plumbing inspector. Just thought I'd see if anyone may know off the top of their head.
 
That's what I'm showing for the fixture count, 1:20. So with an occupant load of 2,936 (1468 per sex) I'll need 74 water closets per sex?? Really?? Something's not right.
 
That is high. IBC is 1/500 if I'm not mistaken.

Out of curiosity, ...

Codegeek said:
... I have an occupant load of 2,804. ...
2 hours later...

Codegeek said:
... So with an occupant load of 2,936 (1468 per sex) I'll need 74 water closets per sex?? ...
... what are you using for occupancy calculations?
 
Yes, Alora, IBC is 1/500 for both men and women in an M use group. This particular project is a mixed occupancy of M/S-1 with some accessory A-2, so using 1/30 for the M, 1/300 for the S-1 and 1/15 for the A-1. The entire project is close to 100,000 square feet,therefore the high occupant load. Both the UPC and the Chicago Plumbing Code would require more fixtures than the IPC in this setting, but to have a 1:20 ratio just doesn't make any sense.
 
I don't know about the MAPC, but IL has its own plumbing code and has a separate occupant load chart for figuring number of occupants. Maybe MA has a different method of calculating occupant load.

Building Type or OccupancyFloor Area per

Person (Sq. Ft.)
Assembly Places – Facilities for Spectator Events; Worship Places and Funeral Homes 15
Museums, Libraries, Exhibition Areas and Similar Uses 50
Schools 50
Day Care Centers 70
Office Buildings200
Food Service Establishments, Clubs, Taverns, and Other Eating/Drinking Facilities 30
Mercantile Units, Except Grocery Stores, Auction Houses, Sale Barns, Car Auction Centers, and other similar Mercantile Units

− First Floor

− All Other Floors



100

120

Combination Grocery Store/Non-Grocery Mercantile Units



150



Mercantile Units, such as Auction Houses, Sale Barns, Car Auction Centers, and other similar Mercantile Units

40



Grocery Stores

200

Storage/Shipping Area400
Power Plants/Industrial Units500
 
Last edited by a moderator:
Thanks TJacobs, I'm familiar with Illinois. I ended up getting a hold of the Building Official who agreed that I was figuring the fixture count correctly based on their code and also agreed that the 70 plus water closets per sex was a bit excessive for a retail establishment.

Thanks for the input and assistance everyone!
 
I know they are pretty tough on plastic pipe and AAV's but looks like you are starting off on the right foot with the AHJ....keep that relationship going and I imagine they will help however they can...
 
I'm still waiting to hear back from the building official who was going to contact the State Plumbing Board for a solution. I hope to have an answer today.
 
In the Mass Plumbing Code (248 CMR) within the minimum fixture chart, I am referring to use group B which states a 33% requirement for male urinals. What exactly does this 33% mean?
 