Sifu
- Joined
- Sep 3, 2011
- Messages
- 3,539
Consider a tenant space with several offices, occupancy B with an occupancy load of 30, that also has two conference rooms, occupancy A with loads of 20 each. 2012 IBC 303.1.2 allows the conference rooms to be considered as part of the B occupancy. Does that entire tenant space require two exits? In other words, would you add the area of the conference rooms to the area of the offices, divide by 100 and get to the occupant load, or calculate them separately, add the number of occupants and provide exits according to that number?
for example:
Calculated separately, the total occ load =70, per t1015.1, 2 exits required from the "space"
3000s.f. offices/100=30
300s.f. conference room/15=20
Calculated cumulatively, 3600s.f./100 =36, one exit required.
Seems like I should know this but I have a problematic T/I and this is part of it. I think I remember that this has been addressed by the code but I can't seem to find it. Code sections will help if there are any.
Seems like just one exit required but I think about a space with lots of small conference rooms and a few offices that could have a much higher occ load trying to get out that one exit. I guess that could change the "accessory" function and maybe flip the calculation.
for example: