Means of Egress Illumination

Abbaad Haider

REGISTERED
Joined
May 18, 2020
Messages
2
Location
Cleveland, OH, USA
The IBC states (1008.2):
The means of egress serving a room or space shall be illuminated at all times that the room or space is occupied.

I have a question regarding the word "serving". I can interpret the above either as:
  1. Referring only to the portion of the MoE up to (but not including) a given room
  2. Referring to the entire MoE from an occupiable space, including portions of the room itself.
Under interpretation #1, it is possible for a person who is standing in a room, furthest from the door not to have a completely illuminated MoE (specifically, the path of egress from that person's location to the door might not be lit).

Under interpretation #2, you can never fully turn off the lights to any space. For example, in a science classroom, the teacher might want to turn off the lights for a demonstration, but 1008.2 would require at least 1fc along the floor throughout the entire classroom. Or similarly, a dark-room for developing photos?

Does anyone know the intent here? Is it interpretation #1 or #2 (or something else)?
 
The Means of Egress states that it starts from any occupied portion of a building and reinforces the concept with the Exit Access.

Note the exception for dwelling and sleeping units.

Note that auditoriums, theaters, concert or opera halls and similar assembly occupancies are allowed to dim the lights Until there is an activation of a fire alarm.

Without the exceptions they would all be lit all of the time. The obvious inference is that all other occupancies lacking an exception shall be illuminated when occupied,

Your second option is the correct choice: “2. Referring to the entire MoE from an occupiable space, including portions of the room itself”

As to a classroom, my experience has been that not all of the lights were turned off. I have no experience with a darkroom but there must be some light or Jeff would spill his coffee and crash something.

Here’s the thing about this. I am just an inspector….. I am not an authority on the subject. Wait for the heavy hitters in the plan check realm before you run with it.
But then I read this again and it seems like a shame to give you all of this information and then tell you not to trust it. I would absolutely believe it.


1008.2 Illumination required. The means of egress serving a room or space shall be illuminated at all times that the room or space is occupied.
Exceptions:
1. Occupancies in Group U.
2. Aisle accessways in Group A.
3. Dwelling units and sleeping units in Groups R-1, R- 2 and R-3.
4. Sleeping units of Group I, R-2.1 and R-4 occupancies.

1008.2.1 Illumination level under normal power. The means of egress illumination level shall be not less than 1 footcandle (11 lux) at the walking surface.
Exception: For auditoriums, theaters, concert or opera halls and similar assembly occupancies, the illumination at the walking surface is permitted to be reduced during performances by one of the following methods provided that the required illumination is automatically restored upon activation of a premises’ fire alarm system:
1. Externally illuminated walking surfaces shall be permitted to be illuminated to not less than 0.2 footcandle (2.15 lux).
2. Steps, landings and the sides of ramps shall be permitted to be marked with self-luminous materials in accordance with Sections 1025.2.1, 1025.2.2 and 1025.2.4 by systems listed in accordance with UL 1994.

MEANS OF EGRESS. A continuous and unobstructed path of vertical and horizontal egress travel from any occupied portion of a building or structure to a public way. A means of egress consists of three separate and distinct parts: the exit access, the exit and the exit discharge

EXIT ACCESS. That portion of a means of egress system that leads from any occupied portion of a building or structure to an exit.


EXIT. That portion of a means of egress system between the exit access and the exit discharge or public way. Exit components include exterior exit doors at the level of exit discharge, interior exit stairways and ramps, exit passageways, exterior exit stairways and ramps and horizontal exits.

EXIT DISCHARGE. That portion of a means of egress system between the termination of an exit and a public way.
 
Last edited:
Thanks for the quick reply ICE.
Note the exception for dwelling and sleeping units. Note that auditoriums, theaters, concert or opera halls and similar assembly occupancies are allowed to dim the lights. Clearly your second option is the correct choice.
I had deliberately left out the exceptions from my question because they were irrelevant to my specific use case, but you're right that their wording strongly suggests interpretation #2.

As far as definitions go, I do of course agree that the MoE begins at any occupied portion, but my question was about "serving" (i.e., can a portion of the MoE serve a room, or does the entire MoE serve the room). Since the Code doesn't seem to emphasize this distinction anywhere else (whereas it is very clear, for example, about the three different parts of the MoE), I think interpretation #2 is likely correct as you say. The same way if you refer to "all the HVAC ductwork serving a specific room", this would include any ductwork in the room itself.
As to a classroom, my experience has been that not all of the lights were turned off. I have no experience with a darkroom but there must be some light or Jeff would spill his coffee and crash something.
I feel like it's not difficult to come up with scenarios of Group E, Group F, or Group I occupancies which require (non-sleeping) people occupying a space in complete darkness. Not too long ago, it wasn't unusual to have darkrooms in American high schools. And yes, a darkroom does require (for at least a small part of the development process) complete darkness (otherwise you would ruin the exposure). There are many other chemical processes (found in laboratory, educational, manufacturing, or healthcare environments) which are similarly light sensitive.

Another issue is that conventional units of illuminance are based upon the photopic luminosity response. But it's possible for some spaces (again darkrooms for a portion of the development process) to use low levels of red light (producing less than 11 photopic lux at the floor), which nevertheless allow an average sighted person to function as well as if it were 11 lux (once their eyes adjust from the photopic regime to the scotopic regime). That is, you can create a situation with 11 scotpic lux at floor level, but less than 11 photopic lux.
But here’s the thing about this. I am just an inspector….. I am not an authority on the subject. Wait for the heavy hitters in the plan check realm before you run with it.
I guess my only remaining reservation is that it just feels weird to completely prohibit an occupant from turning off all the lights in a space, especially when there are plenty of (niche, but not unfamiliar) use cases where this is essential.
 
The building official for state-owned buildings in Virginia clarified IBC 1008 to require "normal power means of egress illumination" (1 footcandle) in restrooms serving more than one occupant and all occupied rooms and spaces 300 square feet and larger. This is in addition to emergency (battery) lights.

We recently did a life safety upgrade to several college classroom buildings and installed 1 or more small LED lights in classrooms, restrooms, & large offices. They are turned on by occupancy sensors and are on circuits with batteries & inverters for emergency power.
 