I thought that it was not permitted to reduce means of egress in the direction of egress travel. Is that so or have I misread or perhaps applied Life Safety Code, where I'm pretty sure that is the case.
I'm looking at 6' wide exit door at second floor from an assembly occupancy to a landing, and from landing to grade is a 5' wide stair. Is that allowed?
I'm looking at 1003.6 (2015 IBC) in particular last sentence: "The minimum width or required capacity of a means of egress system shall not be diminished along the path of egress travel."
Maybe my strict interpretation is wrong, but when I look at the classic large loss of life fires and similar crowd incidents, people jammed up at some restriction is a common theme. The 2003 E2 nightclub in Chicago comes to mind. (Yes, many other contributing factors.)
So set me straight if it's ok for 6' doors to lead to a 5' stair. Yes, I think with the 5' stairs there is still sufficient means of egress capacity for the occupant load, barely.
I'm looking at 6' wide exit door at second floor from an assembly occupancy to a landing, and from landing to grade is a 5' wide stair. Is that allowed?
I'm looking at 1003.6 (2015 IBC) in particular last sentence: "The minimum width or required capacity of a means of egress system shall not be diminished along the path of egress travel."
Maybe my strict interpretation is wrong, but when I look at the classic large loss of life fires and similar crowd incidents, people jammed up at some restriction is a common theme. The 2003 E2 nightclub in Chicago comes to mind. (Yes, many other contributing factors.)
So set me straight if it's ok for 6' doors to lead to a 5' stair. Yes, I think with the 5' stairs there is still sufficient means of egress capacity for the occupant load, barely.