Metal Composite Materials (IBC table 1407.11.3.4)

Paul Sweet

SAWHORSE
Joined
Oct 17, 2009
Messages
2,809
Location
Bedford, VA
IBC 1407.11.3.3.2 defines Class CC1 Metal Composite Materials as having a lower burn rate than class CC2.

Table 1407.11.3.4 allows class CC1 to have a greater % coverage and area than CC2 for fire separation distances of 6 to 30 ft., but lists the maximum area of a CC1 panel with over 30 ft. fire separation distance as "Not Permitted". Shouldn't that say "Not limited"?
 
The table is the same in the 2015 IBC without errata. The commentary for 1407.11.3.2: "Consistent with the requirements for plastic wall panels in accordance with Section 2607.1,"

 