Metal deck

And your issue is grounding?

Wood post/steel deck?

or

steel deck and post?

depending how deep the steel post is embedded in the earth, does it need to be grounded?
 
Last edited by a moderator:
* = * = *



Depending upon which type framing is used, ...IMO, the Manufacturer's

Instructions require grounding.



Also, consider... is the steel framed deck "likely to become energized"

from maybe a lightning event ?



* = * = *
 
north star said:
Depending upon which type framing is used, ...IMO, the Manufacturer's

Instructions require grounding.
Yes they both do, regardless of the " type framing is used".
 
* = * = *



QUESTION:

If you were invited over to one of Dick & Jane's Alcohol-paloozas,

and you were standing on one of these steel framed structures,

...would you want it to be properly grounded ?



* = * = *
 
north star said:
QUESTION:

If you were invited over to one of Dick & Jane's Alcohol-paloozas,

and you were standing on one of these steel framed structures,

...would you want it to be properly grounded ?
I think you are misreading my post.
 
* = * = *



You're darned tootin' I would ! :D

Keystone,

The concensus of 2 have determined that your product is required

to be properly grounded.





* = * = *
 
Either scenario, wood post with steel deck or steel post with wood deck to the top of pier at grade.

I viewed page 27 of the Technical Drawings, no mention of optional grounding which may just be an oversight as the MII does.

Also noted is page 69 of the Manufactures Install Instructions which lists the grounding as optional.

I agree the metal deck whatever the post scenario should be grounded, I am looking for code section to substantiate. Our head electrical inspector is of the opinion grounding is not required, "if a deck is struck by lightning wood or metal you will be hit".
 
& + &

Keystone,

IMO, ...rather than looking in the code book to substantiate the grounding,

...you could reference the manufacturer's web site, Technical Drawings as

the requirement to properly ground their own product.

& + &
 
Under the NEC I would think it would under "building steel" at least need to bonded as a grounding electrode, I do not believe the IRC reads the same.....
 
Keystone said:
. . . Our head electrical inspector is of the opinion grounding is not required, "if a deck is struck by lightning wood or metal you will be hit".
Lightning protection is NFPA 780 typically not a requirement under the building or electrical codes unless adopted.
 
= & = & =



Keystone,

Soooooooo, ...whatcha gunna Option ?.......Ground properly, or not ?

[ Some ] inquiring minds wanna know... :popcorn



= & = & =
 
Attaching a ground rod will not "ground" the deck. Bonding that rod to the grounding electrode system might do the trick. The NEC requires all ground rods to be bonded together but this isn't part of the premises wiring, nor is the deck "likely to be energized." Perhaps it is all about lighting. People that do this must wonder if the Buick should have a ground rod.
 
Last edited by a moderator: