What are some methods to separate a new addition and existing construction if allowable areas are maxed out? Type II-B and we are looking at shaft wall (UL U415 System B). Structural engineer is concerned about using masonry/heavy construction next to the existing building and wants to keep the column line about 3' from existing construction. Regardless of that constraint, is this an appropriate use of shaft wall for a firewall given it is properly detailed?
Also we have a few areas where the existing building and a previous addition were not properly separated. On the newer side they ran 3-5/8" studs with 5/8" gwb-x about 2' from the face of the existing exterior wall. This may be a question for the field inspector but we were thinking we could add shaft liner to the existing furred wall, similar to UL system U505 or U529. Our AHJ has not adopted the IEBC.
Also we have a few areas where the existing building and a previous addition were not properly separated. On the newer side they ran 3-5/8" studs with 5/8" gwb-x about 2' from the face of the existing exterior wall. This may be a question for the field inspector but we were thinking we could add shaft liner to the existing furred wall, similar to UL system U505 or U529. Our AHJ has not adopted the IEBC.