Given:
Type III-B Fully Sprinklered Warehouse building containing Group B and S-1 under 1012 IBC
Under design is a 2,833sf mezzanine which will contain a 996sf enclosed office area along with a 1,837sf storage area. No public access on the mezzanine, just employees of the business and supply storage. Mezzanine will be served by a single, unenclosed stairway. CPET exit distance from most remote corner of mezz to the bottom of stair is 80 feet at which point there are two directions of egress travel available. Our occupant load is 10 + 4 = 14 Occupants total
IBC Code Commentary states that "Because mezzanines that comply with Section 505 are considered a portion of the story in which they are located in accordance with Section 505.2, the exit access stairway leading from it is not required to be enclosed. The enclosure provisions of Section 1009.3 do not apply to stairways that are contained within a single story"
Section 1007.1 requires us to provide one Accessible Means of Egress, which can be a stairway compliant with Section 1007.3 HOWEVER, Section 1007.3 states, "Exit access stairways that connect levels in the same story are not permitted as part of an accessible means of egress"
That seems to say that we can have an open stairway serving the mezzanine, BUT it can not be considered a part of the required Accessible Means of Egress.
Question:
All of that leads to my question, does Section 1104.4 exempt our mezzanine from needing to be accessible, and therefore exempt us from needing to have an Accessible Means of Egress? In other words, does Section 1104.4 trump 1007.1? Section 1104.4 states, "At least one accessible route shall connect each accessible level, including mezzanines, in multilivel buildings and facilities" with Exception 1 reading, "An accessible route is NOT required to stories and mezzanines that have an aggregate area of not more than 3,000sf and are located above and below accessible levels."
A fair amount of counter concepts occuring here making it less than crystal clear. The code seems to say that we DO NOT need an accessible route, but we DO need an accessible means of egress. Similar but different terminology. Bottom line, my question is can we utilize a single unenclosed exit from the mezzanine?
Did my best to make my question as non-confusing as possible, but not sure I succeeded! Thanks to all in advance for your feedback.
Type III-B Fully Sprinklered Warehouse building containing Group B and S-1 under 1012 IBC
Under design is a 2,833sf mezzanine which will contain a 996sf enclosed office area along with a 1,837sf storage area. No public access on the mezzanine, just employees of the business and supply storage. Mezzanine will be served by a single, unenclosed stairway. CPET exit distance from most remote corner of mezz to the bottom of stair is 80 feet at which point there are two directions of egress travel available. Our occupant load is 10 + 4 = 14 Occupants total
IBC Code Commentary states that "Because mezzanines that comply with Section 505 are considered a portion of the story in which they are located in accordance with Section 505.2, the exit access stairway leading from it is not required to be enclosed. The enclosure provisions of Section 1009.3 do not apply to stairways that are contained within a single story"
Section 1007.1 requires us to provide one Accessible Means of Egress, which can be a stairway compliant with Section 1007.3 HOWEVER, Section 1007.3 states, "Exit access stairways that connect levels in the same story are not permitted as part of an accessible means of egress"
That seems to say that we can have an open stairway serving the mezzanine, BUT it can not be considered a part of the required Accessible Means of Egress.
Question:
All of that leads to my question, does Section 1104.4 exempt our mezzanine from needing to be accessible, and therefore exempt us from needing to have an Accessible Means of Egress? In other words, does Section 1104.4 trump 1007.1? Section 1104.4 states, "At least one accessible route shall connect each accessible level, including mezzanines, in multilivel buildings and facilities" with Exception 1 reading, "An accessible route is NOT required to stories and mezzanines that have an aggregate area of not more than 3,000sf and are located above and below accessible levels."
A fair amount of counter concepts occuring here making it less than crystal clear. The code seems to say that we DO NOT need an accessible route, but we DO need an accessible means of egress. Similar but different terminology. Bottom line, my question is can we utilize a single unenclosed exit from the mezzanine?
Did my best to make my question as non-confusing as possible, but not sure I succeeded! Thanks to all in advance for your feedback.