Re: MIC shield
Whoops, I should have said PVC and CPVC. But let Tyco's story tell it all.
http://www.nfsa.org/sq/SQjulaug2009.pdf
From the link above.
Question 1
Tyco Issues Statement on Allied ABF® II and CPVC Pipe In your March 3, 2009 issue (No, 141) you provided an update on the CPVC compatibility issue with regard to antimicrobial coatings on steel sprinkler pipe. Is there anything new this month?
Answer: Yes. Tyco, the parent of Allied Tube and Conduit, issued a release relative to Allied’s ABF® II steel pipe coating
on April 30, 2009, the opening day of the NFSA Annual Seminar and Exhibition. This allowed discussion at workshops on the
topic the following day. In summary, the release explains that in a small number of cases, components of the coating in combination with high levels of mechanical stress may contribute to environmental stress cracking of downstream CPVC
piping. As a conservative approach while its investigation continues, Tyco is recommending that ABF II coated steel pipe not
be used in new systems containing CPVC.
http://alliedtube-sprinkler.com/TycoUpd ... _7166.aspx
See also
http://www.lubrizol.com/BuildingSolutio ... cerns.html