Member
2009 IBC
Existing building is Type IIA - Fire Sprinklered
Mixed Use B/M Non-Separated
5 stories tall.
M is most restrictive, increase to minimum 5 floors per 504.2
We are going to do a office build-out on levels 4 & 5, problem is we will have large conference rooms (bigger than 750 sq ft) on level 4 & 5, which will have to be counted as A-3 Assembly space.
Trying to use it as an accessory occupancy per 508.2, I run into the problem that Type IIA for A3 group has a limit of 3 stories height, so per section 508.2.3 It's impossible because the floor we're building out is on level 4 & I'm not allowed to use any height increase with the sprinklers.
Next is separated occupancy per section 508.4, I need to separate the Assembly from Business with 1 hr assemblies vertically & horizontally. Section 508.4.3 says the allowable height needs to per Table 503, but this time it doesn't specifically say that we're not allowed to use the height increase with the sprinkler, so I'm assuming I can increase the height to 4 & able to put an Assembly space on that level???
Am I correct in my assessment, I can put a large Assembly space on level 4 in a Type IIA sprinklered building using the separated occupancies option? Can y'all let me know if I'm missing anything.
Thanks,
Existing building is Type IIA - Fire Sprinklered
Mixed Use B/M Non-Separated
5 stories tall.
M is most restrictive, increase to minimum 5 floors per 504.2
We are going to do a office build-out on levels 4 & 5, problem is we will have large conference rooms (bigger than 750 sq ft) on level 4 & 5, which will have to be counted as A-3 Assembly space.
Trying to use it as an accessory occupancy per 508.2, I run into the problem that Type IIA for A3 group has a limit of 3 stories height, so per section 508.2.3 It's impossible because the floor we're building out is on level 4 & I'm not allowed to use any height increase with the sprinklers.

Next is separated occupancy per section 508.4, I need to separate the Assembly from Business with 1 hr assemblies vertically & horizontally. Section 508.4.3 says the allowable height needs to per Table 503, but this time it doesn't specifically say that we're not allowed to use the height increase with the sprinkler, so I'm assuming I can increase the height to 4 & able to put an Assembly space on that level???
Am I correct in my assessment, I can put a large Assembly space on level 4 in a Type IIA sprinklered building using the separated occupancies option? Can y'all let me know if I'm missing anything.
Thanks,