I have an existing F-1/B building that is partially sprinklered (currently separated with a 3-hr fire barrier). Total 36,370sf. We are going to sprinkler the whole building as we technically have a COO in expanding F-1 into the current non-sprinklered portion of the building that is open space. There is office space that is also getting expanded into the leftover open space (B). They want to add a large break room that is most likely going to be more than 750sf or 50 persons. I have a few questions....
1) Now that the whole building is sprinklered, we should not need the 3-hr. fire barrier and would be able to punch some holes into it to open up the new F-1 space to the existing?
2) Since my break room is going to be larger than what is allowed under a B occupancy, I would need to consider it an A-3 (most likely will be around 1,000-1,300sf. Would the provisions of 508.3 for non-separated occupancies apply? We are under the A-3, sprinklered, IIb area of 38,000sf? Could it be considered accessory to the F-1 since that is the main purpose of the building?
F-1: 25,490sf
A-3: 1,300sf
B: 7,000sf
S-1: 2,580sf (this is in the basement, constructed of block walls and a precast plank floor)
Total building area: 36,370sf
1) Now that the whole building is sprinklered, we should not need the 3-hr. fire barrier and would be able to punch some holes into it to open up the new F-1 space to the existing?
2) Since my break room is going to be larger than what is allowed under a B occupancy, I would need to consider it an A-3 (most likely will be around 1,000-1,300sf. Would the provisions of 508.3 for non-separated occupancies apply? We are under the A-3, sprinklered, IIb area of 38,000sf? Could it be considered accessory to the F-1 since that is the main purpose of the building?
F-1: 25,490sf
A-3: 1,300sf
B: 7,000sf
S-1: 2,580sf (this is in the basement, constructed of block walls and a precast plank floor)
Total building area: 36,370sf